Actually I would say under almost all circumstances for single-phase...where no testing is performed.Yes it is.
Under certain circumstances
I would phrase it differently as in the UK almost all protection is line-only, and if supply is swapped then every circuit is only limited by the supply fuse.However a live to E fault may not be detected by the protective devices if the polarity is wrong as the current will not be flowing through them.