It sounds to me then that you have 2 different circuits in this room one of which is likely to be a radial but this can only be confirmed by proper testing.
It sounds to me then that you have 2 different circuits in this room one of which is likely to be a radial but this can only be confirmed by proper testing.

How do you tell if a socket is on a ring with a broken leg, vs on a radial circuit? Neither of my two bedroom sockets can be a simple spur since I don't believe a spur off a spur is allowed (is it?) and both sockets have mains in and mains out.
I've encountered this in a property where I was changing a socket in the kitchen.
What had actually happened was at some point in the past, work had been carried out and the two legs of two rings had been interchanged so there was one leg from each RFC in each of the two MCBs that were supposed to be for upstairs and downstairs.
Nearly got a belt off it.
Circuits were unidentified in the CU, so systematically turned them off until I found the one which isolated the socket I was going to work on (left my socket tester in and listened for the beeps to stop), when it went off, unplugged it and turned all the others back on. Thankfully, I double checked with my AVI and was glad I did![]()
if you post your location, one of us may be close enough to pop round and have a gander. usually, most will not charge for an initial assessment of the situation and will be upfront with a quote for any costs before incurring them.That sounds extremely plausible... and a bit worrying, therefore.
That sounds extremely plausible... and a bit worrying, therefore.
What I will add is that before I simply re-connected them correctly, I tested both of them to ensure that both rings were continous (end to end continuity) and there were no interlinks elsewhere. Once reconnected, they both got a basic earth fault loop impedance test (with a sample of the outlets) to ensure that was up to scratch once connected properly.
This is not something you should do without proper test equipment and knowledge.
I agree with @telectrix 's suggestion, give us a clue on your location and see if you can get one of us in to have a look.
Just to put it into perspective, the fix I did took about an hour (mainly because of the testing) and cost my client less than £50.
It requires proper test equipment and an experienced spark.
It requires proper test equipment and an experienced spark.
How do you mean "takes it personal" if the OP isnt experienced or qualified, may be , just may be the best bet would be to hire an Electrician, wouldn't want to tell someone how they think something should be done and the persons ends up killing himself , would we??I love how everyone takes it personal on this forum page an instantly hits up the "consult a qualified spark " outlook

I love how everyone takes it personal on this forum page an instantly hits up the "consult a qualified spark " outlook
Just to put it into perspective, the fix I did took about an hour (mainly because of the testing) and cost my client less than £50.