Discuss Isolate circuit but trips fuse board in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Non-contact voltage detectors are NOT to be used to prove a circuit is dead.
I would strongly advise getting a set of two pole voltage detectors, test before isolation to prove working,
isolate, prove dead, then retest detector to prove still working.
thanks. I have a multimeter - can I use that instead? And what would the test be, just that there is no voltage from either Live or Neutral when compared to Earth or something else? thanks again.
 
It's linked to why the RCD tripped. The N conductor is connected to other N conductors inside the consumer unit.
It is possible (should any of a number of things happen upstream, inside or outside your house or with the supply) for the current path of other circuits in your house to go via the socket circuits N wire, via you, to earth.

This reason was why I said "or better use the main switch". @Risteard is spot on that really it should be the only approach in your situation.
You might get away with it 99.9% of the time, but if the supply N happens to break at the wrong moment, it's curtains time!

(This is one of a number of reasons why new consumer units that I fit have double pole isolation on each circuit and separate RCD protection for each circuit. They are much easier to do maintenance on!)

There are other reasons too related to the average experience of DIY people doing this, that would not necessarily apply in your case.
thanks, appreciate advice. the consumer unit is about 15 years old. would you recommend I upgrade the consumer unit so it has double pole isolation and separate RCDs as it is not very practical to turn off the mains each time i want to work on a circuit? or is there another solution? thanks.
 
Think of it this way Elisa 100. Live current flows out of your meter, via the consumer unit, through all of your circuits and flows back through the neutral wires. This flowing current will be used when you have an appliance or light switched on.

All the neutral circuits are directly connected together in your consumer unit using a metal bar in that consumer unit. Same applies to all of the earth wires (which modern electricians may call a CPC).

Your Circuit Breaker (MCB M being for Miniature) in your case is interrupting the live circuit that it is attached to, but is NOT interrupting the neutral circuit. Current is flowing (returning) through the entire neutral circuit in your house as you will have lights on as you said and maybe appliances in use (eg washing machine) on different circuits.

So even on the circuit you think you have isolated, your neutral remains connected to the rest of the neutrals on live circuits.

If you touch a neutral on your isolated circuit to earth, the residual current circuit breaker (RCCD) in the consumer unit will detect this as a leakage of current. As a leakage could for all it knows be current flowing through you to earth (ie you are getting an electric shock) it plays safe and trips all power off everywhere.

I am a DIYer too and I expect qualified professionals could explain it better than I have. Personally I do not work on circuits without isolating the neutral as well. My consumer unit has a type of switch that does that and I can also isolate the consumer unit totally from the meter if I need to with a simple switch as well. In your case I would turn everything fully off at the main switch and use a battery powered light to assist you if that is needed. Electricity is a killer so don’t take risks.

By the way, non contact voltage protectors are less than ideal for identifying when something is live or not (unreliable and give a false sense of security at times), and will not identify anything that is only potentially live. There are more suitable testers that will be much safer - but obviously that incurs expense and you need to know how to check them and use them.
thanks - useful advice.

So am I right in understanding there is always a current flowing through the neutral wires - including the circuit which has been broken - as long as at least one circuit is live and/or unless the main switch is off?
 
also - is using a mains wiring socket tester - the one which plugs into a socket which checks for mis-wiring (I have the Kewtech KEWTECH 103 - OK instead of using a voltmeter / multimeter to show the lines are not live?
 
The reason for using a test lamp is it's easier to prove that they are working correctly. If you isolate the RCD, none of your sockets will be working , so unable to prove correct operation.
 
The reason for using a test lamp is it's easier to prove that they are working correctly. If you isolate the RCD, none of your sockets will be working , so unable to prove correct operation.
Yes, but my question is about whether a mains wire tester is (together with turning off the circuit at the MCB) a safe alternative to turning off the main switch (when changing a plug socket etc)? I am not sure if it is?
 
It isn't. As has been pointed out, the mcb only isolates the line conductor.
Isolating the RCD or main switch isolates both line and neutral.
Is your D.B. the same as the one in the video?
 

Reply to Isolate circuit but trips fuse board in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock