cctbreaker

What do folks find is best way to satisfy 17th on a bathroom install that has no supp bonding and no rcd on lighting? (The spur feeding the jacuzzi will be rcd protected) Do you go for the supp bonding or fit an RCD to lighting circuit?
Steve
 
Yes, that was the next thought. It's a split load brd and we could move the 6A MCB over onto the RCD side but then we are making the separation of circuits worse. Could put in an rcbo instead.
 
If theres no supp bond there already lighting RCBO would be a way of satisfying regs . Or just had a thought. If the supply to the bathroom is in plastic pipe there is no need to supp bond. If it's in copper cut the supply pipes to the bathroom (turn the water off first!!) and fit either a short length of plastic 15/22 or plastic pushfit couplers this will interrupt the metal in the bathroom from the metal in the rest of the house. we're not worried about conductivity of water only metal. You'd also need to do the same to any rads or towel rails. If you need further advice on water isolation depending on the type of dhw system let me know exactly what you've got there and I'll tell you the quickest and easiest way of doing it.
 
If theres no supp bond there already lighting RCBO would be a way of satisfying regs . Or just had a thought. If the supply to the bathroom is in plastic pipe there is no need to supp bond. If it's in copper cut the supply pipes to the bathroom (turn the water off first!!) and fit either a short length of plastic 15/22 or plastic pushfit couplers this will interrupt the metal in the bathroom from the metal in the rest of the house. we're not worried about conductivity of water only metal. You'd also need to do the same to any rads or towel rails. If you need further advice on water isolation depending on the type of dhw system let me know exactly what you've got there and I'll tell you the quickest and easiest way of doing it.

be much easier to move the mcb :)
 
Had a similar install recently. Luckily everything was on RCD so no supp. bonding, but the Tub motor had a flying earth on it. Where did you take that to??? The pipes for the hot and main to the tub are plastic, but the g&y must be there for a reason! Would be appricate since I still have access to the tub.
 
if you are only installing the jacuzzi you dont have to touch the lighting circuit you are only obligated to rcd the jacuzzi.
 
Had a similar install recently. Luckily everything was on RCD so no supp. bonding, but the Tub motor had a flying earth on it. Where did you take that to??? The pipes for the hot and main to the tub are plastic, but the g&y must be there for a reason! Would be appricate since I still have access to the tub.

The one I'm doing doesn't have a flying earth (well not that I noticed on my prelim visit). I guess it may be included on yours for any supp bonding you might want to do.
 

Reply to Jacuzzi install in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627
Just a thought guys in terms of RCBO’s and supplementary bonding. Obviously supplementary bonding isn’t required as long as a 17th / 18th...
Replies
5
Views
2K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
401
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock