providing its all tidy and insulated, could someone please explain why the suggestion of using a single strand into a wago would be frowned upon.
Electrically, of course, it would be fine. It's the ethics that are screwed up here. Leaving strands out of a termination violates a fundamental rule that is deeply imprinted in any (good) electrician's brain. Plus the Wago instructions would probably be disobeyed in two or three different ways.
A technically correct solution would be as suggested by Shaun1, to terminate the two cables into appropriate-sized DIN terminals and link them with commoning bars. Or to crimp on some suitable ring terminals (e.g. 6mm hole) and connect them via DIN-rail mounted insulated stud terminals. I have used that method before, for widely disparate cables sizes. There are all sorts of halfway house options, like lap crimps. Soldering, if done with skill, could make a nice job of it.
But I might still go for the 1-strand-in-a-Wago. In an outdoor terminal box, the less exposed metal and fewer things to corrode or create leakage, the better. From a purely engineering standpoint, provided the heatshrink job is well executed, it might be the most suitable technique. I leave for the reader the agonising consideration of inter-strand resistance after a few years of moisture ingress, vs. the equalisation of current between strands along the length of the cable.