Have 18th ed and page 505 does say an unfused spur should feed one twin socket outlet. However if a 13amp fused spur is then connected to this and then to another socket is this not permissible? I can't see any potential for cable overloading? Thanks
 
Depends where the 13A FCU was positioned along the spur ? If after the double outlet then possible load could be 39A. Or am I misunderstanding ?
 
Depends where the 13A FCU was positioned along the spur ? If after the double outlet then possible load could be 39A. Or am I misunderstanding ?
I think you might of understood me correct Andy and my calculations are not right. At moment it goes ring main, then goes to spurred off socket. Then thinking I might of been able to from here to 13amp spur then to double socket. Would this then possibly give a 39Amp load from socket on the ring?
 
I think you might of understood me correct Andy and my calculations are not right. At moment it goes ring main, then goes to spurred off socket. Then thinking I might of been able to from here to 13amp spur then to double socket. Would this then possibly give a 39Amp load from socket on the ring?
Yes. 2 x 13A at double socket and 13A from the spur. I'm assuming the cable size is 2.5mm with a ref method C rating of 27A ?
 
I think you might of understood me correct Andy and my calculations are not right. At moment it goes ring main, then goes to spurred off socket. Then thinking I might of been able to from here to 13amp spur then to double socket. Would this then possibly give a 39Amp load from socket on the ring?

This is not permitted, the fused spur must be before the first twin socket to make this compliant.
 
Yes. 2 x 13A at double socket and 13A from the spur. I'm assuming the cable size is 2.5mm with a ref method C rating of 27A ?
It would of been if installed yes. The potential for overloaded cables are then the ones on the ring then which could be drawing 39amps? Just for my own clarity the fact that it is a ring and wired in 2.5mm parrellel does this have any bearing on what max amperage the ring is capable of drawing. Cheers
[automerge]1580162318[/automerge]
This is not permitted, the fused spur must be before the first twin socket to make this compliant.
Cheers for confirmation Dave
 

Reply to Just checking my understanding of spurs off rings in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock