Hi gents and ladies,

I’ve just bought a Kewtech KT63, the instructions aren’t very clear on lead setup. When doing a Ze is this a 3 lead test on no trip setting, using the green blue and brown test leads? When doing PEFC and PSCC is this a 2 lead test on high setting. So the blue/green leads connected together on the earth or neutral bar and the brown lead on line?

Thanks
 
Low current/no trip type tests should only be used when absolutely necessary due to the presence of an RCD.

When measuring Ze you should always use a high current test.
 
I have a KT63 though don't use it much now.
When doing a Ze is this a 3 lead test on no trip setting, using the green blue and brown test leads?
No. High current 2 lead test (green and blue joined together) between Line and disconnected main earth, with the installation isolated.
When doing PEFC and PSCC is this a 2 lead test on high setting,
So the blue/green leads connected together
Yes.
So the blue/green leads connected together on the earth or neutral bar and the brown lead on line?
Yes regarding connecting leads together. I usually do PSCC at the top of the incomer.

The low current loop tests are 3 wire tests. As above, they very tremendously in accuracy.
This video shows a handy workaround that is well worth knowing.
 

Reply to Kewtech KT63 lead setup for ze, pefc and pscc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I was asked to go and take a look at a generator set up by a marquee company yesterday to do some testing. It was a brand new JCB 65QS with...
Replies
7
Views
2K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
416
I have a fairly typical setup of the light on my landing being able to be controlled by both a switch on the landing and a switch at the bottom of...
Replies
1
Views
2K
I hope someone can help me as im getting different answers off different people 3P & N Supply Ze: Disconnect main earth Set tester to 2 lead...
Replies
29
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock