I’ve just bought a Kewtech KT63, the instructions aren’t very clear on lead setup. When doing a Ze is this a 3 lead test on no trip setting, using the green blue and brown test leads? When doing PEFC and PSCC is this a 2 lead test on high setting. So the blue/green leads connected together on the earth or neutral bar and the brown lead on line?

Thanks
 
Low current/no trip type tests should only be used when absolutely necessary due to the presence of an RCD.

When measuring Ze you should always use a high current test.
 
I have a KT63 though don't use it much now.
When doing a Ze is this a 3 lead test on no trip setting, using the green blue and brown test leads?
No. High current 2 lead test (green and blue joined together) between Line and disconnected main earth, with the installation isolated.
When doing PEFC and PSCC is this a 2 lead test on high setting,
So the blue/green leads connected together
Yes.
So the blue/green leads connected together on the earth or neutral bar and the brown lead on line?
Yes regarding connecting leads together. I usually do PSCC at the top of the incomer.

The low current loop tests are 3 wire tests. As above, they very tremendously in accuracy.
This video shows a handy workaround that is well worth knowing.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Kewtech KT63 lead setup for ze, pefc and pscc
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Sookme,
Last reply from
Markyd,
Replies
3
Views
3,340

Advert

Back
Top