hi whilst testing ELI on lighting circuits, using kewtech kt63 on loop no trip function, test keeps tripping rcd once polarity and voltage is confirmed. I know the kt63 tests at 250v in this mode, but it shouldn’t trip the rcd, anyone else experienced this? Is it calibration time? Is it me? Is it the rcd? Anyone’s thoughts, and I know the calculation is Zs =(Ze + r1r2), a bit frustrated the damn things keep tripping, upstairs and downstairs, separate circuits, separate rcds, both trip.
 
hi whilst testing ELI on lighting circuits, using kewtech kt63 on loop no trip function, test keeps tripping rcd once polarity and voltage is confirmed. I know the kt63 tests at 250v in this mode, but it shouldn’t trip the rcd, anyone else experienced this? Is it calibration time? Is it me? Is it the rcd? Anyone’s thoughts, and I know the calculation is Zs =(Ze + r1r2), a bit frustrated the damn things keep tripping, upstairs and downstairs, separate circuits, separate rcds, both trip.
Watch the R1R2 thing r1,rn and r2 are endto end readings of a ring final circuit
Zs= Ze+(R1+R2) your formula is wrong
 
Hi - did you unplug everything and turn off lights from the final circuits supervised by the RCD ? (as there may be loads with leakage)
Yeah even down to disconnecting separate cooker hood circuit from mcb. Needed doing anyway to do fused switch change and test, so not a hassle but still same result, all light bulbs removed everything.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Prestatyn
Business Name
FLS

Thread Information

Title
Kewtech kt63 no trip function
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Paddington,
Last reply from
happysteve,
Replies
20
Views
12,297

Advert

Back
Top