Discuss Kewtech kt63 no trip function in the UK Electrical Forum area at ElectriciansForums.net
hi whilst testing ELI on lighting circuits, using kewtech kt63 on loop no trip function, test keeps tripping rcd once polarity and voltage is confirmed. I know the kt63 tests at 250v in this mode, but it shouldn’t trip the rcd, anyone else experienced this? Is it calibration time? Is it me? Is it the rcd? Anyone’s thoughts, and I know the calculation is Zs =(Ze + r1r2), a bit frustrated the damn things keep tripping, upstairs and downstairs, separate circuits, separate rcds, both trip.
Watch the R1R2 thing r1,rn and r2 are endto end readings of a ring final circuit
Zs= Ze+(R1+R2) your formula is wrong
Hi - did you unplug everything and turn off lights from the final circuits supervised by the RCD ? (as there may be loads with leakage)
Yeah even down to disconnecting separate cooker hood circuit from mcb. Needed doing anyway to do fused switch change and test, so not a hassle but still same result, all light bulbs removed everything.
My 63 has been a great buy, this one is strange. No doesn’t have ramp the 65 is a step up from the 63.
Um! The KT63 DOES have ramp test. It's on the little button top left with the x1/2, x1 and x5.
See picture...
If you're into the CU, perhaps dis the RCD outputs and test separately?
That’s a possible, rcds tested well though, highest 34ms at 1x lowest 14ms at 5x not overly quick or sensitive. No trips at 1/2. Whole installation is good and tests as you would hope to expect!
See picture...
doh yes of course it does! Deliberate mistake, honest.
I've never had a problem where my KT63 trips an RCD on no-trip loop (so far - not saying it'll never happen), though I have had issues where it refuses to take a test. This has usually turned out to be a problem with the neutral... for instance, this socket-outlet had a decent R1+R2 value, but would not do a no-trip Zs
You can see the degradation on the neutral terminal.
If you're having trouble measuring Zs on an RCD circuit, you can always use "The Alternative Method for Measuring Zs," using "high current loop" setting.
Reply to Kewtech kt63 no trip function in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
6K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
14K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
4K