Search the forum,
Discuss kitchen cooking appliances cable size in the Australia area at ElectriciansForums.net
Hi just about to have a oven 3.6kw,combi microwave 3.6kw,hob 6.6kw fitted,the electrician is splitting the original 6mm cable to seperate isolation points for these appliances,my doubt is ,is this cable big enough electrician assures me if the diversty is taken into consideration the cable is big enough,and also states a 6mm cooking cable within the new regulations is allowed upto 15kw,can someone let me know if this is correct
well generally with ovens....you take the first 10A....then 30% of whats left.....now then...if the cooker switch (double pole) has a BS1363 outlet on it...just add 5A......
he's right. you have 13.8KW. that equates to 60A. applying diversity... 10A + 15A = 25A . so 6mm on a 32A MCB is fine .
thanks for that i shall be able to sleep now,knowing that when he turns up tomorrow it is going to be okay.the cable is under upstairs flooring so imagine insulation is little or none,Thanks
Reply to kitchen cooking appliances cable size in the Australia area at ElectriciansForums.net
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
4K
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
  • Locked
5K