Yes total load decreases but the imbalance increases, as I say not looked into the phase for many moons. Just remember we had to balance it best as possible
Yes it will become imbalanced but that doesn't increase the load!
With an unbalanced load there will be some neutral current, but with simple resistive loads the neutral current will never exceed the line current no matter how far out of balance it is.
Didn't explain very well but I was thinking of the neutral current.You can only have a neutral of reduced csa if your line conductors are of a minimum csa of 16.0, copper conductor.
You can only have a neutral of reduced csa if your line conductors are of a minimum csa of 16.0, copper conductor.
I won't be running 16mm for ufh 
Never heard of it.Interesting, I haven't really looked at it since I encountered 3 1/2 core SWA used for TPN quite a few years ago.
Can you still get 3 1/2 core SWA?
I thought I was getting oldInteresting, I haven't really looked at it since I encountered 3 1/2 core SWA used for TPN quite a few years ago.
Can you still get 3 1/2 core SWA?
, never heard of that though.Is this a three core with a half sized neutral.Interesting, I haven't really looked at it since I encountered 3 1/2 core SWA used for TPN quite a few years ago.
Can you still get 3 1/2 core SWA?
Never heard of it.
Is this a three core with a half sized neutral.
Never seen that looks like AWA.