Did some tests yesterday with my new alphatek 775 on some kitchen appliances that were sometimes tripping a 30ma rcbo. Went straight to the main suspect which was the washing machine, plugged it into lead i made up with conductors out of sheathing and clamped live conductors and got a reading of 22mA. Then did the same for the other appliances and and got some more high readings so i went to cu and clamped the kitchen ring cpc's, switched all appliances on and got 37mA and rcbo didnt trip. Ramp tested rcbo and it tripped at 20mA. Am i doing something wrong? Tester was set to 200mA range, should it be 2A? IR tested the circuit before and got >299 megohms.
Just been trying it at home and it seems to be picking up current outside the jaws giving me exaggerated results. Think I'm gonna send it back.
Leakage current tester results?
Periodic Inspection Reporting & Certification
cakey,
cakey,