Discuss leakage test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

A

ample current

I tested a washing mashine today and it failed the leakage test.
What it the relationship of this test to an insulation test?
It gave a reading of 0.76mA
The insulaton test was good with >20M Mohms
amd earth continuity was ok too.

Any insight would be nice please.
 
Did you retest it? If so was it the same again?
Awkward thing to run and then try again, but did you do this?
I would like to know the answer myself..
 
What it the relationship of this test to an insulation test?

There is not always neccessarily a relationship, as the IR test is carried out with DC, and the leakage test is carried out with AC, things like filter/suppression and motor start/run etc. capacitors which allow some AC to pass normally, but block DC (normally) can skew the results somewhat.
 
Last edited:
If this washing machine has electronics on board then I would be testing for an upper limit of 3.5mA. This machine would therefore pass on this particular test.
 

Reply to leakage test in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
640
Hi, I carry out PAT testing on landlord appliances for letting agents in rented accommodation. Occasionally some of the items I cannot access...
Replies
5
Views
694
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
293
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Replies
12
Views
1K
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
637

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock