D

Dumkopf

I am adding an upper storey to my existing two storey house. It would certainly make sense to put the additional lighting circuit on its own mcb at the CU but is that a Part P requirement?
 
not a part p requrement, but BS7671 has a reg.( forget the no.) about division of curcuits to minimise danger/inconvenience when 1 circuit fails, so it would be the better option to have both lights and sockets for the new floor eachon their own circuit.
 
not a part p requrement, but BS7671 has a reg.( forget the no.) about division of curcuits to minimise danger/inconvenience when 1 circuit fails, so it would be the better option to have both lights and sockets for the new floor eachon their own circuit.
Many thanks telectrix. Much obliged to you.
 
part p compliance should be achieved through his biulding contol for the build. BC can inspect electrical work as part of the project.
 
as i read the OP. he's asking if it's a requirement to put lights on a new circuit or not. ifhe does, new circuits fall under part p. if he doesn't, he falls foul of the division of circuits reg, up to a point. if ground floor lights and 1st floor lights are on separate circuits, it 's not a crime to add 2nd floor lights to 1st floor light circuit.. (he'll need to watch out for low flying aircraft though. o_O o_O o_O ).
 
I understood that "but is that a part P requirement?" was referring to whether the new floor lighting should have its own circuit, or a separate circuit. It was nothing to do with whether it is notifiable or not.
 
part p compliance should be achieved through his biulding contol for the build. BC can inspect electrical work as part of the project.

Part P wouldn't be an issue if just extending existing circuits into a new build extension, only if installing a new circuit(s) from the CU.
[automerge]1577617607[/automerge]
I understood that "but is that a part P requirement?" was referring to whether the new floor lighting should have its own circuit, or a separate circuit. It was nothing to do with whether it is notifiable or not.

I guess we all interpret the questions differently when not exactly very clear in the OP's question.
 
My interpretation of the Op's question is;

'If I put in a new lighting circuit for the new storey, is that subject to notification under Part P'?

Which of course would be yes but I see the view others are taking which is also correct in that it is NOT a requirement of Part P to put in a new circuit!
Perhaps I'm reading too much into it!
 
My interpretation of the Op's question is;

'If I put in a new lighting circuit for the new storey, is that subject to notification under Part P'?

Which of course would be yes but I see the view others are taking which is also correct in that it is NOT a requirement of Part P to put in a new circuit!
Perhaps I'm reading too much into it!

How on earth did you get that from the OP's question?
There is no mention of notification, no mention of if,

Yes I think you are reading too much into it, you're guessing at what might be the motivation behind the question, or what the next question might be rather than just reading what is written in black and white in front of you.
 
@Dumkopf
As well as the lighting question, are you aware that, when you make your house 3-storey, you will need to install interlinked smoke alarms on all storeys of the house?
I guess you have a building notice for this work? You need to make sure this sort of thing is covered, or your friendly Building Control operative will be less than friendly.
 
How on earth did you get that from the OP's question?

As I said we all have our own interpretations of an Op's question!
Perhaps I should have said NO its not a requirement of Part P
BUT
If you (Dumkopf) go for the new circuit option, notification under Part P is required!
 