The earth on the incoming cable(s) may not actually be connected to earth, but could be floating somewhere between 0 and 240V depending on the loading. If you are going to connect the earth to the fitting, you need to be sure the incoming earth actually is connected to earth, otherwise you would be leaving the fitting as potentially dangerous.
You can test this - with the power to the installation turned off - for example with the aid of a long lead back to the main earth terminal and a multi-meter set to measure Ohms.
I also agree that with the wiring as photographed, it should not be class II - you have single insulated cables inside the ceiling rose, that might touch the metal casing - and if you accidentally caught one e.g. by a sharp edge or screw, it could pierce the insulation. It is difficult to install it to meet class II with the loop in/out extra wires, unless you also double insulate these and the connector block.
You can test this - with the power to the installation turned off - for example with the aid of a long lead back to the main earth terminal and a multi-meter set to measure Ohms.
I also agree that with the wiring as photographed, it should not be class II - you have single insulated cables inside the ceiling rose, that might touch the metal casing - and if you accidentally caught one e.g. by a sharp edge or screw, it could pierce the insulation. It is difficult to install it to meet class II with the loop in/out extra wires, unless you also double insulate these and the connector block.