Costumer have 12 flats and need to feed for each flat a prepaid meter and consumer unit within the flat , the main supply to building is three phase , my question is how to distribute the load for 12 flats, each flat have a load of 63A.
Main supply is three phase .
 
TL;DR
Hello
What exactly do you want help with here?

How you distribute the supply is via a suitable distribution board, I believe ryefield boards are the most commonly used for this application.
 
What exactly do you want help with here?

How you distribute the supply is via a suitable distribution board, I believe ryefield boards are the most commonly used for this application.
Thank you for reply.
I spoke to costumer to fit 12ryefield board with 63A fuses , but he bought it live three phase board with 125A main switch rating and 12 , 63A MCBs to make the cost cheaper.
My question is if I installed that it will be ok for load demand .
 
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?

Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
 
Last edited by a moderator:
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?

Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 10A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?

Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?

Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
Thank you for the information , because it’s three phase it will be 125 x 2 = 250A .
 
For the first item which is shower full 100% load 40A and the rest 56 x 0.4 = 21.6
40+21.6= 61.6 A

I mean discrimination between supply MCB and shower MCB/RCBO. The reason for asking is that I believe the rule of thumb to achieve discrimination between MCBs is that upstream needs to be at least 2x the rating of that being supplied.

Happy to stand corrected.
 
I mean discrimination between supply MCB and shower MCB/RCBO. The reason for asking is that I believe the rule of thumb to achieve discrimination between MCBs is that upstream needs to be at least 2x the rating of that being supplied.

Happy to stand corrected.
I think as longer the load is not exceeding the main breaker load it’s ok , protective device must be equals or greater .
 
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?

Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
If four residents on the same phase took a shower at the same time, this would be the case on a 125A incomer. Are there diversity rules to be applied between dwellings on the same phase though?

I don't think the OP has yet supplied the specification of the incomer though, only that the main switch for the three phase board purchased is rated at 125A.
 
Last edited:
I think as longer the load is not exceeding the main breaker load it’s ok , protective device must be equals or greater .
It sounds like you are well out of your depth here.

a 3 phase board with 125A INCOMER can handle
3 x 125A
not
2 x 125 = 250A

your first action should be to meet the designer and decide on what the load per flat is going to be.

next decide if the existing supply is capable of providing this for 12 flats.
if not, apply for a suitable supply to be installed.

this all needs designing from the ground up, not lashed together with bits from the car boot and hope it works.
 