Thank you for reply.What exactly do you want help with here?
How you distribute the supply is via a suitable distribution board, I believe ryefield boards are the most commonly used for this application.
He didn’t provide me with any info from DNO .What have the DNO specified?
What does the design specification state.
each flat have a 8.5kw shower, 16A sockets, 32A cooker and 6A lights . I calculated it all load is 61.6A .What does the design specification state.
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?
Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 10A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated
As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?
Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
Thank you for the information , because it’s three phase it will be 125 x 2 = 250A .As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?
Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
Thank you for the information , because it’s three phase it will be 125 x 2 = 250A .
For the first item which is shower full 100% load 40A and the rest 56 x 0.4 = 21.6Would discrimination present an issue where 40A shower circuit is supplied from 63A MCB?
For the first item which is shower full 100% load 40A and the rest 56 x 0.4 = 21.6
40+21.6= 61.6 A
I think as longer the load is not exceeding the main breaker load it’s ok , protective device must be equals or greater .I mean discrimination between supply MCB and shower MCB/RCBO. The reason for asking is that I believe the rule of thumb to achieve discrimination between MCBs is that upstream needs to be at least 2x the rating of that being supplied.
Happy to stand corrected.
If four residents on the same phase took a shower at the same time, this would be the case on a 125A incomer. Are there diversity rules to be applied between dwellings on the same phase though?As an apprentice my posts here should not be taken as advice, but as questions from someone who wishes to learn and what I'd really like to learn is how a 125A incomer might ever be considered suitable for a block of 12 flats?
Putting maximum demand to one side; if 4 residents happen to take a morning shower at the same time, that 125A incomer is going to be handling its full rated current before any other consumption is factored. If each flat were to draw an average 15A at any given time (not an unlikely situation), then the incomer is handling far in excess of its rated current.
It sounds like you are well out of your depth here.I think as longer the load is not exceeding the main breaker load it’s ok , protective device must be equals or greater .