Iv got a little install of 2 IP rated sockets to go on an exterior wall of a log cabin. The customer doesn't want to see any cables or containment as you look at the sockets. We've agreed to run black PVC conduit on the rear of the cabin (which is going to have shrubs growing up it) and then back entry into the 2 socket outlets.

The issue I have is from an installation view. The cabin panels are 20mm thick. Installing a female conduit bush and then a 90° bend will leave the conduit far to long to then fix to the back of the cabin and then run the lengths.

Would it be better to use a short piece of flex out of the socket just to get a tight 90°?

A few drawings below which may help

IMG_20190625_080506.jpg

IMG_20190625_080637.jpg
 
don't fit a bend. fit a conduit end box with a hole drilled in back. silicon to prevent water ingress wher cable goes from box through wall.
 
Upvote 0
Reading the OP again, and this time understanding what is required, I would go for end box - through box - end box from the CU, 1st socket, 2nd socket.
Or IP rated adaptable boxes

Watch the length of any screws into the wall if its only 20mm thick
 
Upvote 0