Hi just a quick question if doing long lead r2 test would touching a pin on a socket prove that it’s earthed for example? And if it did would it be accurate? Also on the eicr forms I seen it says you have to put a value for either r1+r2 or simply R2, I know you do the long lead R2 test for gas and water but is it acceptable to do it for others too?
Thanks
 
You can use method 1 or method 2 to confirm R2

Using something that is earthed does not confirm the presence of R2, it just confirms a path to earth.

However, it's worth noting containment can be used as a cpc. You need to be sure what it is your connecting to and what it is your trying to confirm.
 
The R1+R2 or R2 columns are found on the EIC, Minor works certificate and a condition report. It should be appreciated that the R2 test alone does not confirm polarity unless you have physically removed the accessories to access the connections and you will have to directly measure the Zs rather than doing the calculated Zs method, if that’s your preference to obtain Zs that is?
 
Thanks for the replies, so I was reading the regs and it said about if there is a fixed lug then the pin will earth the back box so I thought that then it’s possible to get a R2 reading from a pin, but was wondering how accurate it would be compared to getting a reading directly from the earth taking the socket off etc.
 
If this is for doing an EICR then that’s one way to confirm that an earth is present at an accessory without dismantling it but for the purpose of writing it in the R2 column as a measured result,then all parallel paths would be required to be disconnected and it’s better to test at the connection itself but it is not something that’s necessary on an EICR, a earth fault loop impedance test would be the required method.
All other methods are not precluded of course
 
, i wander lead test on the screw heads of each accessory just to confirm presence of earthing. do an accurate R2 at the last point (mid point on a RFC). bugger with dry line boxes though.
 
, i wander lead test on the screw heads of each accessory just to confirm presence of earthing. do an accurate R2 at the last point (mid point on a RFC). bugger with dry line boxes though.
Thanks for the reply, is there much difference in the reading if you test the screw head the testing the actually earth itself?
 
very little as long as the screws make good conract . not guaranteed to be accurate though. it's a handy method of mapping out a circuit though, due to the fact that R2 will increase from point to point, the further along you get from the CU.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

DeanoRN

Trainee
-
Joined
Location
Birmingham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Long lead R2 test
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
DeanoRN,
Last reply from
baldelectrician,
Replies
8
Views
144

Advert

Back
Top