okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.
put it down to bad 1 croc clip &1probe.
 
okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.

Why are you doing it at the sockets? The pfc reading needs to be at the DB not the ends of the circuit.

The variations at the origin are likely to be down to the inaccuracy of the meter and possible poor test leads or contact pressure.
 
@davesparks i did do pfc at the board but its habit of always flicking dial round to test pfc on individual circuits too, something i was taught in college as an extra check, whether correctly or not and have done it ever since. i do think with the kewtech testers though it might be acceptable to do at sockets, might be wrong.... it was demonstrated at one of them tradefairs once with kt63 doing pfc at sockets to check individual circuits.... was couple years back mind. the guy did a zs at the socket then pressed a button to get psc/pfc...
 
The 64DL is limited compared to the KT65DL which can give readings down to 0.001, but switching off ATT will likely provide a more accurate Ze reading.
 
are your leads okay? might sound stupid but I got in a right muddle with my KT63 last week! was testing sockets in a house and getting 0.73 zs on one socket, then on others on the same ring stupidly low readings like 0.03 and massive kA!!!! I would have thought dodgy leads should have increased the reading but for some reason it didn't! cracked out some fresh leads and everything stabilised and all sockets tested near enough the same at 0.73....

with the substation so close though its entirely possible that it isn't reading too far off!

My thought too!
 
Could I just ask why you are taking a Ze reading, I assume this was made by removing the red link between the cut out and meter?
If so this comes under Mocopa or DNO rules and should not be done unless you have the required authorisation to remove the red link, anything on the load side of the meter feel free to test.
 

Reply to Lower Ze reading than expected in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I've had an unusual result from taking a Ze at a clients house and wondered what everyones take on it would be: The property is TN-C-S A Ze...
Replies
9
Views
4K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock