On a job today and when testing got a Ze of 0.03 ohms on a tncs. Using a Kewtech 64DL.

Installation has main fuse in hallway outside the 2 bedflat then a switched fuse feeding a submain cable to the actual CU. I did Ze at both immediately before switched fuse and in CU with earth disconnected each time. Both times got 0.03 ohms even with the submain cable running 6 metres.. given the MFT;s have a margin of error this is a pain, I have checked the tester on a calibration box and it measures 1 ohm fine. it looses half an ohm at 100 ohm reading on loop test according to calibration box.

Zs@DB is 0.12 ohms... only utility feeding the property is a district heating system with metal pipes running through building into ground and heating building next door, these pipes are 4 inch diameter into building and around floors into water re heater boiler by flat entrance. the water is fed via plastic pipes. so would provide a very good parallel earth

The building is just over 2 years old and is just up road from the transformer.

Due to low Ze i am also getting funny and varying PFC PSCC readings which would if readings are correct then i have a very high lpf..... Have attached some images to explain better... Am wondering if leads might be playing up? MFT is only a month old out of the box... might use the R2 lead to add some extra resistance then take it off values when i go back tomorrow.
Any thoughts?

20170914_145319.jpg 20170914_145328.jpg 20170914_153702_HDR.jpg 20170914_153755.jpg 20170914_153900.jpg 20170914_154135.jpg 20170914_154311.jpg 20170914_154926.jpg
 
Was the main earth disconnected when you carried out your testing?
 
  • Informative
Reactions: tim barnard
Yes main earth was disconnected as it entered switch fuse enclosure, its shown in the image coming from cutout to the 16mm bolt where it joins the submain cable that feeds CU in flat. i disconnected it here to do Ze and then reconnected and did Ze again in the consumer unit with it disconnected from earth bar.
 
Last time I had that with a Kewtech 65dl was 0.03 Ze. I spoke with Kewtech tech. and they pointed out of course that is + or - 6 digits which it does say in the manual. I questioned it because apart from the high pfc the DNO had just installed a new cut out and testing with a megger they got 0.11 As kewtech said well if you add on 6 digits you are at .09 which is nearly the same as the DNO. So make what you will of that. All I can say is when you are measuring hundreths of an ohm things get a bit indistinct. And yes the sub station was within a hundred yards.
 
  • Like
Reactions: Jon H
Last time I had that with a Kewtech 65dl was 0.03 Ze. I spoke with Kewtech tech. and they pointed out of course that is + or - 6 digits which it does say in the manual. I questioned it because apart from the high pfc the DNO had just installed a new cut out and testing with a megger they got 0.11 As kewtech said well if you add on 6 digits you are at .09 which is nearly the same as the DNO. So make what you will of that. All I can say is when you are measuring hundreths of an ohm things get a bit indistinct. And yes the sub station was within a hundred yards.
Well it should be better outlined or resolved by kewtech, in this case the flats im working in are only 100m from the transformer that feeds the development. its possible there is another sub unit in under the building that splits off to each meter or within the underground carpark.
 
Well it should be better outlined or resolved by kewtech, in this case the flats im working in are only 100m from the transformer that feeds the development. its possible there is another sub unit in under the building that splits off to each meter or within the underground carpark.
Does it comply?
 
  • Like
Reactions: Vortigern
Looking at the 9.69kA PFC your Ze is even lower if you do the maths, around 0.023 ohms.

As long as the breaking capacity of the OCPD are good then no problem.

However the variance Kewtech claim raises ones eyebrow a little...
 
0.03 ohms is below 0.35 so complies but my lpf is over the breakers at 6ka are no good if we are going by the regs... think its 432 something off top of my head - might be wrong.. im getting varying pfc and pscc readings even with tails held in croc clips rather than probes.... only difference being i press the test button again! ; i suspect either the MFT is not reading correctly or within its margin of error.
 
Sorry, I'm a bit lost here - what measures at 0.12 ? And then you get impedance dropping to 0.03 when you go further from the cut out into a flat? Can you explain again, cheers.
 
Sorry, I'm a bit lost here - what measures at 0.12 ? And then you get impedance dropping to 0.03 when you go further from the cut out into a flat? Can you explain again, cheers.
sorry .. 0.03 ohms is Ze measured at both the switched fuse and again in the flat , each time having the earth disconnected, the first time at Switched Fuse and the Second at the earth bar so really Ze@db. the 0.12 ohms is Zsdb in the flat... which i would expect to be higher given the large metal pipes that feed the heating system across the development which are linked into the earth bar with a 10mm earth cable.
 
However the variance Kewtech claim raises ones eyebrow a little...
it is no good if you can not trust your mft giving you false reading.
 
  • Agree
Reactions: Strima
bin the kewtech.
upload_2017-9-14_18-0-23.png


upload_2017-9-14_17-59-17.png
 
  • Funny
Reactions: Strima
In work we have nearly 20 MFTs so could justify buying the Megger test box, cracking bit of kit that gives us the option to test loop impedance. I have to say all the Meggers and Metrels we have are always within range. The Flukes can be a little more temperamental.

I don't think we'll be buying Kewtech in the near future...
 
  • Agree
Reactions: buzzlightyear
Keep in mind I've now started pain killing rituals here, but I'm lost again. I got 0.03 as Ze measuring L-E with the earth dis from the board, but why does it rise to 0.12 when the other bonding is included?
In work we have nearly 20 MFTs so could justify buying the Megger test box, cracking bit of kit that gives us the option to test loop impedance. I have to say all the Meggers and Metrels we have are always within range. The Flukes can be a little more temperamental.

I don't think we'll be buying Kewtech in the near future...
Mine works perfect, always has, always will . Hang on, just gotta go sacrifice a fatted lamb or summat.
 
Keep in mind I've now started pain killing rituals here, but I'm lost again. I got 0.03 as Ze measuring L-E with the earth dis from the board, but why does it rise to 0.12 when the other bonding is included?

Mine works perfect, always has, always will . Hang on, just gotta go sacrifice a fatted lamb or summat.
I thought the 0.12 was the Zdb not the Ze???
 
I was harf way thru that post when this joyous IT device posted it. B thing has a mind of its own, maybe that's a good thing ..
 
are your leads okay? might sound stupid but I got in a right muddle with my KT63 last week! was testing sockets in a house and getting 0.73 zs on one socket, then on others on the same ring stupidly low readings like 0.03 and massive kA!!!! I would have thought dodgy leads should have increased the reading but for some reason it didn't! cracked out some fresh leads and everything stabilised and all sockets tested near enough the same at 0.73....

with the substation so close though its entirely possible that it isn't reading too far off!
 
okay 0.03 ohms is the Ze i get whether i test Ze at CU or the switched fuse as its technically origin... the 0.12 ohms is ZSdb which given the flat is serviced by huge metal pipes for the district heating which are bonded its got a parallel path of some substance! the heating system has a boiler type thing which is fed by the pipes and if i run a continuity test on the boiler pipes i can connect to one next door in their cupboard and get a beep.
If it helps anybody understand i have had copies emailed to me from the original install certificates by the owner. back then they only got a Ze of a 0.11 and the Zs values for circuits are pretty much what i got today, maybe a fraction out in some cases. if you look at the Zs values they are all quite low. so i suspect the flat has never had much of a Ze to begin with.if i do a PFC or PSCC pluged in at the sockets i get more sensible readings but at the CU they are all over.
i have blocked out the cert number to stop cowboys copying for fakes...

View attachment cert1.jpeg

View attachment cert2.jpeg
 
are your leads okay?
I am thinking that might be the case, so might buy some new ones to be sure... at very least it gives a comparison for the current ones. interestingly if i use the plug lead to test my readings are more stable
 
now who would do a thing like that.
cowboys lurk everywhere... homebase or screwfix carparks, on checkatrade and trustedtrader and even down your local pub... they are out there hiding ready to rip off somebody at a moments notice with a freshly ebay sourced scam logo on their van...
 
I've missed that the switch fuse is 0.03 and further away in the flat you get Zdb 0.12 (?). Anyway, with 0.12 all your protective devices are within their breaking capacity so that's ok? If the impedance reading is suspicious (with very low numbers), perhaps try adding a known resistance cable in series?
 
  • Agree
Reactions: buzzlightyear
you missed one home on the range .
 
@Wilko , yes thats correct Ze at Switched fuse of 0.03 and a Zs @ DB of 0.12. I am going to get a 2nd set of leads and compare and then do what you suggest, but when i look at the original EIC (I uploaded them as images) the original readings were also very low. mine are too far out the norm compared to these assuming the original firm tested correctly.
 
High resistance readings through the switch fuse contacts?
What was the R1+R2 reading on the submain?

A lot of my work colleagues use a kewtech and this problem of accuracy at low resistance testing was highlighted at a large installation on student accommodation we installed.
When carrying out a R1+R2 test on a 120mm submain to a block when using the kewtech on 2 separate kewtech meters the result was 0.00ohms.
When tested with my own megger 1552 mft I got a reading of 0.04 ohms.
We also tested other blocks some 150mm submains and one was 240mm.
Kewtech constantly read 0.00 whole the megger had readings of around 0.03 and 0.02 respectively. Submains varied in lengths but the kewtech couldn't read the low resistance continuity tests unlike the megger.
Just an example
 
Last edited by a moderator:
  • Informative
Reactions: Gavin John Hyde
@Ian1981 I haven't as yet done a R1+R2 on submain, which maybe is my poor terminology as its feeding the Cu from the switched fuse as tails would be too long otherwise, I wasn't expecting to have the results i have had so far in all honesty. i was only adding a circuit in for a heated towel rail! They aren't too far from original install tests looking at the cert from owner.
I get 0.03 ohms even testing Ze before the switch fuse with the earth disconnected from the bolt in switched fuse enclosure and testing on incoming line/ neutral. you can see what i mean in the pics in my original post on thread. i took earth out from the 16mm bolt for the Ze.
 
0.03 ohms is below 0.35 so complies but my lpf is over the breakers at 6ka are no good if we are going by the regs...

But you said the Zdb is 0.12 ohms, so the prospective fault current at the DB is going to be around 2kA, well within the capability of a 6kA mcb.
The switched fuse at the origin will have a fuse with a much higher breaking capacity so that will almost certainly be fine too.
 
But you said the Zdb is 0.12 ohms, so the prospective fault current at the DB is going to be around 2kA, well within the capability of a 6kA mcb.
The switched fuse at the origin will have a fuse with a much higher breaking capacity so that will almost certainly be fine too.
okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.
 
okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.
put it down to bad 1 croc clip &1probe.
 
  • Agree
Reactions: Gavin John Hyde
okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.

Why are you doing it at the sockets? The pfc reading needs to be at the DB not the ends of the circuit.

The variations at the origin are likely to be down to the inaccuracy of the meter and possible poor test leads or contact pressure.
 
  • Like
  • Agree
Reactions: Davisonp and Wilko
@davesparks i did do pfc at the board but its habit of always flicking dial round to test pfc on individual circuits too, something i was taught in college as an extra check, whether correctly or not and have done it ever since. i do think with the kewtech testers though it might be acceptable to do at sockets, might be wrong.... it was demonstrated at one of them tradefairs once with kt63 doing pfc at sockets to check individual circuits.... was couple years back mind. the guy did a zs at the socket then pressed a button to get psc/pfc...
 
The 64DL is limited compared to the KT65DL which can give readings down to 0.001, but switching off ATT will likely provide a more accurate Ze reading.
 
  • Agree
Reactions: Wilko
are your leads okay? might sound stupid but I got in a right muddle with my KT63 last week! was testing sockets in a house and getting 0.73 zs on one socket, then on others on the same ring stupidly low readings like 0.03 and massive kA!!!! I would have thought dodgy leads should have increased the reading but for some reason it didn't! cracked out some fresh leads and everything stabilised and all sockets tested near enough the same at 0.73....

with the substation so close though its entirely possible that it isn't reading too far off!

My thought too!
 
  • Agree
Reactions: Pete999
Could I just ask why you are taking a Ze reading, I assume this was made by removing the red link between the cut out and meter?
If so this comes under Mocopa or DNO rules and should not be done unless you have the required authorisation to remove the red link, anything on the load side of the meter feel free to test.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Gavin John Hyde

Esteemed
Arms
Patron
~
Joined
Location
Somerset
Website
http://www.sulis-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Sulis Electrical Services Ltd

Thread Information

Title
Lower Ze reading than expected
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
Gavin John Hyde,
Last reply from
stevels4,
Replies
36
Views
11,597

Advert