Discuss Lower Ze reading than expected in the UK Electrical Forum area at ElectriciansForums.net
I've missed that the switch fuse is 0.03 and further away in the flat you get Zdb 0.12 (?). Anyway, with 0.12 all your protective devices are within their breaking capacity so that's ok? If the impedance reading is suspicious (with very low numbers), perhaps try adding a known resistance cable in series?
@Wilko , yes thats correct Ze at Switched fuse of 0.03 and a Zs @ DB of 0.12. I am going to get a 2nd set of leads and compare and then do what you suggest, but when i look at the original EIC (I uploaded them as images) the original readings were also very low. mine are too far out the norm compared to these assuming the original firm tested correctly.
High resistance readings through the switch fuse contacts?
What was the R1+R2 reading on the submain?
A lot of my work colleagues use a kewtech and this problem of accuracy at low resistance testing was highlighted at a large installation on student accommodation we installed.
When carrying out a R1+R2 test on a 120mm submain to a block when using the kewtech on 2 separate kewtech meters the result was 0.00ohms.
When tested with my own megger 1552 mft I got a reading of 0.04 ohms.
We also tested other blocks some 150mm submains and one was 240mm.
Kewtech constantly read 0.00 whole the megger had readings of around 0.03 and 0.02 respectively. Submains varied in lengths but the kewtech couldn't read the low resistance continuity tests unlike the megger.
Just an example
@Ian1981 I haven't as yet done a R1+R2 on submain, which maybe is my poor terminology as its feeding the Cu from the switched fuse as tails would be too long otherwise, I wasn't expecting to have the results i have had so far in all honesty. i was only adding a circuit in for a heated towel rail! They aren't too far from original install tests looking at the cert from owner.
I get 0.03 ohms even testing Ze before the switch fuse with the earth disconnected from the bolt in switched fuse enclosure and testing on incoming line/ neutral. you can see what i mean in the pics in my original post on thread. i took earth out from the 16mm bolt for the Ze.
0.03 ohms is below 0.35 so complies but my lpf is over the breakers at 6ka are no good if we are going by the regs...
But you said the Zdb is 0.12 ohms, so the prospective fault current at the DB is going to be around 2kA, well within the capability of a 6kA mcb.
The switched fuse at the origin will have a fuse with a much higher breaking capacity so that will almost certainly be fine too.
okay, maybe i haven't explained things too well. I appreciate the replies... my confusion come from doing pfc and psc and getting varying results as shown in the pictures. when doign a pfc plugged into the sockets on rfc's i was getting 2.4kA and 2.65kA. both well within limits i cant explain the variation in readings the kt64 was giving out at CU.
Reply to Lower Ze reading than expected in the UK Electrical Forum area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
4K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...