On a job today and when testing got a Ze of 0.03 ohms on a tncs. Using a Kewtech 64DL.
Installation has main fuse in hallway outside the 2 bedflat then a switched fuse feeding a submain cable to the actual CU. I did Ze at both immediately before switched fuse and in CU with earth disconnected each time. Both times got 0.03 ohms even with the submain cable running 6 metres.. given the MFT;s have a margin of error this is a pain, I have checked the tester on a calibration box and it measures 1 ohm fine. it looses half an ohm at 100 ohm reading on loop test according to calibration box.
Zs@DB is 0.12 ohms... only utility feeding the property is a district heating system with metal pipes running through building into ground and heating building next door, these pipes are 4 inch diameter into building and around floors into water re heater boiler by flat entrance. the water is fed via plastic pipes. so would provide a very good parallel earth
The building is just over 2 years old and is just up road from the transformer.
Due to low Ze i am also getting funny and varying PFC PSCC readings which would if readings are correct then i have a very high lpf..... Have attached some images to explain better... Am wondering if leads might be playing up? MFT is only a month old out of the box... might use the R2 lead to add some extra resistance then take it off values when i go back tomorrow.
Any thoughts?
20170914_145319.jpg 20170914_145328.jpg 20170914_153702_HDR.jpg 20170914_153755.jpg 20170914_153900.jpg 20170914_154135.jpg 20170914_154311.jpg 20170914_154926.jpg
Yes main earth was disconnected as it entered switch fuse enclosure, its shown in the image coming from cutout to the 16mm bolt where it joins the submain cable that feeds CU in flat. i disconnected it here to do Ze and then reconnected and did Ze again in the consumer unit with it disconnected from earth bar.
Last time I had that with a Kewtech 65dl was 0.03 Ze. I spoke with Kewtech tech. and they pointed out of course that is + or - 6 digits which it does say in the manual. I questioned it because apart from the high pfc the DNO had just installed a new cut out and testing with a megger they got 0.11 As kewtech said well if you add on 6 digits you are at .09 which is nearly the same as the DNO. So make what you will of that. All I can say is when you are measuring hundreths of an ohm things get a bit indistinct. And yes the sub station was within a hundred yards.
Well it should be better outlined or resolved by kewtech, in this case the flats im working in are only 100m from the transformer that feeds the development. its possible there is another sub unit in under the building that splits off to each meter or within the underground carpark.
Does it comply?
Looking at the 9.69kA PFC your Ze is even lower if you do the maths, around 0.023 ohms.
As long as the breaking capacity of the OCPD are good then no problem.
However the variance Kewtech claim raises ones eyebrow a little...
0.03 ohms is below 0.35 so complies but my lpf is over the breakers at 6ka are no good if we are going by the regs... think its 432 something off top of my head - might be wrong.. im getting varying pfc and pscc readings even with tails held in croc clips rather than probes.... only difference being i press the test button again! ; i suspect either the MFT is not reading correctly or within its margin of error.