Even if all the circuits in the bathroom are RCD/RCBO protected?

Sent from my GT-I9300 using Tapatalk 2

In this case, all pipes should be bonded to the incoming line conductor.... upstream of the service fuse!
 
the building is all in plastic speed fit is it not?

quote o/p,
"Water comes in on 15mm copper where there is a 300mm length BEFORE IT IS THEN CONVERTED TO PVC SPEEDFIT"

​
 
Last edited by a moderator:
Fella's

I was told today by a spark a lot more experienced than me that I need to bond the following, I'm inclined to agree but could do with some opinions.

Water comes in on 15mm copper where there is a 300mm length before it is then converted to PVC speedfit,this whole section is hidden in a cupboard, it does go back to copper eventually.

Is it worth bonding that small section?

Listen to the Spark that has a lot more experience than yourself, as well as the experienced guy's on here that are telling you exactly the same thing!! lol!!
 
bond within 600mm of the stop, nothing to stop someone for changing the plastic back to copper in future.

only omitt the bonds if it is a full (entering and throughout) pvc installation
 