essexboy

hi all thanks reading my post

i have just changed a Cu and intend on using the job for my elecsa inspection i have up-graded the meter tails from 16mm to 25mm ,the earth conductor ( TN-S ) looks like 6mm and needs to be upgraded to 16mm ,but who should be up grading the earth conductor?? is this down to the dno?? or should i just upgrade from the cu met to the met outside the cu ??
 
If the mec is terminated to the incommer lead/sheath I tend to cut it to a short length & terminate into a met/block (with a 951 label fixed to it) that I fix to the meter backboard. From this met I run 16mm to the cu.
Then advise the customer (backed up with a letter sent with certs) that they need to contact dno to upgrade the mec.
 
thanks easyfox ,as i thought but just needed someone elses opinion which is what i love about this site
 
"Then advise the customer (backed up with a letter sent with certs) that they need to contact dno to upgrade the mec."

Probably wont upgrade as they will claim that it is sized by calculation. If you use the adiabatic equation to check you will probably find that the 6mm is ok, but best to use EasyFox's installation method.
 
yeah it is appropriate but when your viewing threads you know who people are by there avatar (i do anyway!) Easy's easy going but dont know if you might be better finding sommat a little bit different? lol

how bout this

Main earth conductor?? {filename} | ElectriciansForums.net


blimey thats big!!
 
Last edited:

Reply to Main earth conductor?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock