Could the Neutrals for the socket circuits be mixed up with the socket circuit on the other side of the board? This would mean you are connecting 1 leg of each circuit into the rcd side that's tripping and causing an unbalanced load.
 
Could the Neutrals for the socket circuits be mixed up with the socket circuit on the other side of the board? This would mean you are connecting 1 leg of each circuit into the rcd side that's tripping and causing an unbalanced load.
OP are there 2 lighting circuits if yes could be he has got crossed Ns ie N for up stairs and down stairs crossed, try swapping the Ns over, let us know how you get on.
 