We have recently purchased a home in TX built in the 1920s, and the wiring is an assortment of multiple wiring events. There aren't any local codes as it is unincorporated land. The events in question are with the overhead wiring to the pole barn subpanel consisting of two 10 gauge solid-core wires, one hot and one neutral with no ground. After an intense storm, the support for the wiring broke free from the house and caused the wires to hang dangerously low. At this point, I cut the wires where they exited from the house attic. Now it is time to restore power back to the barn, but I know there are issues with its current configuration and need some assistance. I may use the term subpanel incorrectly as it might be considered a feeder, so please just insert the proper term as it applies.

There is currently a tray cable with three black insulated 10 gauge wires that go from the service panel on the house, up into the attic, and out the other side. One is connected to a 20amp breaker, one is connected to the neutral bus, and the other is currently not connected to anything (it wasn't used all the way to the barn). The service panel neutral and ground bars are bonded.

The subpanel in the barn only had two wires going into it, the hot and neutral, only supplying 120v which I'm ok with.. The neutrals and grounds from the barn circuits are both connected to an insulated neutral bus in the subpanel. No grounding rods are installed at the barn. Now that the current setup is established, here's what I want to do.

I have buried PVC conduit 20 inches below the surface to run UF cable underground instead of suspended. The distance between the side of the house and barn is 25ft. I plan to attach the loose 3rd wire to the service ground bar (properly labeling it as a ground) and use the other two wires as the hot and neutral (labeling it also). These will terminate at a new unbonded subpanel on the other side of the house. From this subpanel, I want to run UF 12/2 w ground to the barn subpanel. I'm assuming I would need to isolate the grounds from the neutral bar and check all barn grounds aren't connected to neutral, establishing an emergency path back to the service panel. I'm guessing I would also need to attach two grounding probes to the barn subpanel as well. I've heard you can ground to the metal barn, but I'm not certain if there are metal water pipes that run to the house that would cause an unintentional parallel line.

I know the current configuration is not to code and may have never been. Is it worth the trouble to execute my plan, or should I just reconnect the hot and neutral, except this time run them in separate conduits underground to the barn? If neither sounds right to you or you have suggestions or improvements, I'm all ears! Ideally, I would run new 10/3 w ground the whole way, but it's too expensive to go that route. Other options may be to just purchase a single 10ga ground and run it out to the barn or use a GFCI at the service panel and label the outlets not grounded? Although going up to code is unlikely, whatever I can do to make it safer is a step in the right direction.

I know this is a little confusing, and I will be more than happy to clarify anything for you. I want to bring the wiring closer to code than it is. Fun with old houses never ends.
 
We have recently purchased a home in TX built in the 1920s, and the wiring is an assortment of multiple wiring events. There aren't any local codes as it is unincorporated land. The events in question are with the overhead wiring to the pole barn subpanel consisting of two 10 gauge solid-core wires, one hot and one neutral with no ground. After an intense storm, the support for the wiring broke free from the house and caused the wires to hang dangerously low. At this point, I cut the wires where they exited from the house attic. Now it is time to restore power back to the barn, but I know there are issues with its current configuration and need some assistance. I may use the term subpanel incorrectly as it might be considered a feeder, so please just insert the proper term as it applies.

There is currently a tray cable with three black insulated 10 gauge wires that go from the service panel on the house, up into the attic, and out the other side. One is connected to a 20amp breaker, one is connected to the neutral bus, and the other is currently not connected to anything (it wasn't used all the way to the barn). The service panel neutral and ground bars are bonded.

The subpanel in the barn only had two wires going into it, the hot and neutral, only supplying 120v which I'm ok with.. The neutrals and grounds from the barn circuits are both connected to an insulated neutral bus in the subpanel. No grounding rods are installed at the barn. Now that the current setup is established, here's what I want to do.

I have buried PVC conduit 20 inches below the surface to run UF cable underground instead of suspended. The distance between the side of the house and barn is 25ft. I plan to attach the loose 3rd wire to the service ground bar (properly labeling it as a ground) and use the other two wires as the hot and neutral (labeling it also). These will terminate at a new unbonded subpanel on the other side of the house. From this subpanel, I want to run UF 12/2 w ground to the barn subpanel. I'm assuming I would need to isolate the grounds from the neutral bar and check all barn grounds aren't connected to neutral, establishing an emergency path back to the service panel. I'm guessing I would also need to attach two grounding probes to the barn subpanel as well. I've heard you can ground to the metal barn, but I'm not certain if there are metal water pipes that run to the house that would cause an unintentional parallel line.

I know the current configuration is not to code and may have never been. Is it worth the trouble to execute my plan, or should I just reconnect the hot and neutral, except this time run them in separate conduits underground to the barn? If neither sounds right to you or you have suggestions or improvements, I'm all ears! Ideally, I would run new 10/3 w ground the whole way, but it's too expensive to go that route. Other options may be to just purchase a single 10ga ground and run it out to the barn or use a GFCI at the service panel and label the outlets not grounded? Although going up to code is unlikely, whatever I can do to make it safer is a step in the right direction.

I know this is a little confusing, and I will be more than happy to clarify anything for you. I want to bring the wiring closer to code than it is. Fun with old houses never ends.
You say you already have a conduit to your barns sub panel. It needs to be 4 wire and needs to GFCI protected. If you pull your ground from your house panel and hook it up in your sub panel you can get rid of the ground rods. You should have 2 bars in your barn panel so you can keep the grounds and neutrals isolated from each other. I feel what your up against but at least this will make it safe. If the barn is metal then you can ground it out off your sub panel to the ground bar. Good luck my friend
 
You say you already have a conduit to your barns sub panel. It needs to be 4 wire and needs to GFCI protected. If you pull your ground from your house panel and hook it up in your sub panel you can get rid of the ground rods. You should have 2 bars in your barn panel so you can keep the grounds and neutrals isolated from each other. I feel what your up against but at least this will make it safe. If the barn is metal then you can ground it out off your sub panel to the ground bar. Good luck my friend
Thanks for the extra push to go ahead and run a 4 wire configuration and the reminder for a GFCI. I was trying to get away with not having to run an extra wire through the attic, but it's the smart move. If you're going to do it, you might as well do it right!

Thanks again!
 

Reply to Making 10/2 w/o Ground Pole Barn Subpanel Safer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm starting a new construction single-family residence, I know with the 2020 NEC they require an emergency disconnect on the exterior of the...
Replies
5
Views
2K
I have an old 1959 house that appears to have outside service panel feeding 2 subpanels in the house each with only 3 wire feed. One subpanel(A)...
Replies
3
Views
829
Just getting ready to wire up this 100 amp subpanel., The subpanel is being fed from the meter base, not the main panel in the house. It doesn't...
Replies
3
Views
1K
I have an outbuilding a fair distance from the house. In this outbuilding I just want to have some lights, a small music radio/clock, and a...
Replies
0
Views
523
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
999

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock