No, MK Board, 32a RCBO (Downstairs Ring only) then 63a RCD (Cooker/boiler/DS Lights) 2nd 63a RCD (US Ring/US Lights)

So the down stairs ring final has a fault to earth?. Have you done any IR tests. Any appliances that could be causing earth leakage?
 
wait until a day off, have everything as it is. when it trips make a note of the time and try turning it straight back on. is the central heating on the same circuit?

It was, but when we go away we turn it to low temp so it only comes on if temp drops below 16deg, I was wondering wether the temp drop could affect it, was looking for a 7day 24hr mechanical timer, so I could identify when it trips
 
So the down stairs ring final has a fault to earth?. Have you done any IR tests. Any appliances that could be causing earth leakage?
IR tested okay, not tested any appliance, I'm starting to feel as though an appliance may be the cause, havn't spent enough time on it, as fair new to this, initially I just assumed it was with somthing I had done, is there a test I can do with appliances plugged in then take them out one by one to try and identify the culpret?
 
Have you tested the rcd for nuisance tripping?? I know you have tried on both rcd and Rcbo but maybe (I always say if it can then it will) they are both faulty!! Try x0.5 with rcd trip time tester and it shouldn't trip.
Other than this is there something damp when the temp drops when your away??
Leave the cold set on the house by leaving temp drop and carry out another I.R test and see if there is anything down to earth?? Maybe rain is getting in and doesn't dry out when your away!

Mmm these ones can be tricky!!
 
X5 part of standard testing, both RCDs & RCBO tested fine, will ramp test them, IR testing with the heating off was a thought, but not sure I can stand a couple of days without heating ;)
 
why would it take a few days to IR test an installation.
I think you misunderstood me, I know if I do any insulation tests right now it would be fine, but if the temperature is likely to affect it, I would have to switch off the heating, my house is pretty well insulated, so would have to leave it at least 24 hours to drop to the temp it gets to while were away to replicate the situation, I'm only guessing that its temp related, as its now been 3 weeks since we were away and it hasn't tripped since then
 
Make sure you lock all your windows and doors when you go out as it could be a neighbours plugging an extension lead in and running a heater for a few hours to save on their bills.
 
Time to borrow/beg an MFT maybe?
Think you need to read all the post, I have a MFT that how I certified the installation, I have an intermittent RCD trip on the D/S sockets that has happened the last three times I have been away, the changes I can see to the circuit while I am away are reduced load (ie TV's not on etc, kitchen is on different circuit) and the ambient temperature (which is -3 outside at the mo) I have retested the RCD, but not yet done a ramp test

Thanks all, as just going over this in my head is throwing up all sorts of possible ideas of cause!
 
I didn't put it past someone going into the garage (which doesn't have a door on at present) and flicking the switch... to the point of scanning though the CCTV, not this time....
 
Sounds like a load of bull to me, either your competent in electrical installation work and understand testing and fault finding or your a chancer?? which is it??????
 
Another thought have you got a frost stat on the heating that is not coming in when your their and could have a fault when needed
 