I work for an FM company, we’ve just taken on a brand new refitted and rewired premises.

There is a 3phase DB supplying sockets into which there were loads of electronic equipment which has suffered multiple failures. The DB is supplied via 4pole contactor which is switching the Neutral. It’s a TNCS supply and I’m thinking this contactor switched Neutral is the problem. The contactor has now been replace with a 3 pole and solid link to Neutral.

Thoughts??
 
The contactor is for BMS control for energy management.

I should have mentioned the contactor went faulty yesterday and one of the poles was open circuit and perhaps a slack coil supply as it was dropping in and out a couple of days ago.
 
If the equipment is getting damaged due to switching off the supply under fault conditions withe the supply, then I would have though the client should consider UPs backup to allow for a controlled shut down of the electronic equipment, a costly initial outlay, but a money saver in the long run, imo
 
Unless the contactor N pole was late break early make, breaking the Neutral certainly would have caused problems.

Unless it's a perfectly balanced load across all 3 phases, which it won't have been with single phase loads, the phase voltages can rise (and fall) momentarilly at the time of switching.
 
I’m thinking just the action of switching the contactor may have meant that not all 4 poles closed at the exact spilt second and might have cause massive overvoltage in the phases. Or the neutral was open circuit for a time leading to anywhere up to 415v applied in the phases.

I wouldn’t say I’m an expert on this but this is my understanding of it.
 
Sounds a likely cause to me, especially if the contactor has been chattering in and out and maybe going randomly high-resistance in the neutral pole. I've seen more electronics cooked by neutral loss on a TP+N supply than pretty much anything else. Not sure why anyone would think of switching it on a BMS contactor, seeing as you don't even need to switch it on an isolator.
 
in france alot of house have a 3 phase supply and all have the neutral switched and I have never seen a problem but last year in a storm the neutral cable going to a house got broken and there was a lot of damage to electrical equipment in the house, fridge dishwasher, pool pump, a electric air freshiner melted and nearly burn down the house would check all neutral conections and then recheck them,
 
The building is fully BMS operated. There is a valid reason, for which I can’t fully divulge as the electrical contractor may well be part of this community and I would assume there is a large finger pointing exercise about to commence.

We’ve checked the drawings and it should have only been 3 pole. Seems the install contractor took it on themselves to switch the N via 4 pole.
 
BMS systems do not control dist boards for general lighting and power.
 
I work for an FM company, we’ve just taken on a brand new refitted and rewired premises.

There is a 3phase DB supplying sockets into which there were loads of electronic equipment which has suffered multiple failures. The DB is supplied via 4pole contactor which is switching the Neutral. It’s a TNCS supply and I’m thinking this contactor switched Neutral is the problem. The contactor has now been replace with a 3 pole and solid link to Neutral.

Thoughts??
I’m thinking just the action of switching the contactor may have meant that not all 4 poles closed at the exact spilt second and might have cause massive overvoltage in the phases. Or the neutral was open circuit for a time leading to anywhere up to 415v applied in the phases.

I wouldn’t say I’m an expert on this but this is my understanding of it.
hope it's ok to sidetrack a little, we are fitting 4pole contactors on boards at present so staff can have an easy mode of switching off at end of shift. There are lots of gaming machines connected to the circuits most of which have inbuilt computers (I believe) do you think I should connect neutral direct. Thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Renfrew

Thread Information

Title
Massive damage. Neutral fault
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
Michael White,
Last reply from
Farmelectrics,
Replies
20
Views
4,267

Advert

Back
Top