The standards table in the regs states that BS HD 60269-2:2013 fuses can also be numbered BS 88-2:2013, which from table 41.2 would give you a max Zs of 2.43 for a 16A fuse.
The standards table in the regs states that BS HD 60269-2:2013 fuses can also be numbered BS 88-2:2013, which from table 41.2 would give you a max Zs of 2.43 for a 16A fuse.
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc