Hi,
I am looking for a little advise on how to apply diversity and work out maximum demand on a new installation I am designing in a Cabin.
Cabin CU has 3 circuits
Circuit 1
6 Socket outlets - to supply 2.7KW Floor standing Hair dryer
Electric Oil filled radiator
Hand held hair dryer
Kettle
radio
Using 2.5mm T&E and 16 or 20A MCB depending on advise regarding diversity
Circuit 2 Lights - 6 * Fluorescent 58W Lights plus an outdoor 300W floodlight
Using 1.5 T&E 3A MCB
Circuit 3 7.2KW Shower
Using 4mm Flex on 32A MCB
My Main Question is cable size back to the house 20m away
I will be using SWA Buried
Can I apply the 60% rule here ? should cable be rated min 52A ? Is it somewhere in between ?
Any guidance would be appreciated,
Thank you
lets have a look ......
well all your plug in loads are going to exceed 16 / 20 A even with diversity so your gonna need a 32a ring or radial.
and your lighting comes to 4.1a so a 3a mcb is no good either
shower is bog standard 31a jobby.
ignoring diversity for a moment , the biggest limiting factor for cable selection will be volt drop for the lighting , not current capacity.
without doing a load of maths as im just home for work , you should get it all on a 50a type C mcb which will give you a bit of discrimination with the cabin mcb's but cablewise at least 10mm maybe 16mm as a ballpark guesstimate.
i'd also be checking the dno fuse size before commencing work if the cabin supply is being fed from a house.
Hi,
Circuit 1
Kettle
radio
Thank you
instantanious water heater.....no diversity allowed here...
I do, Read it from cover to cover a few times, I know Im only learning and college cannot teach me half of what I need to know,
I was taught on the EIC form to put down 60% of the Total Breaker ratings as Maximum demand !
Is this just the lazy answer ?
OSG is not very clear on the subject ! I am going through 7671 now to try to answer my own questions !
Max demand and diversity is a subject that has no definitive rule book. As far as I know, the only figures that are used regularly are the CIBSE ones.
they give W/m2 from what I'm aware.
as for us normal blokes on the tools, your knowledge of what your installing is the only real way of calculating diversity.
a rule of thumb for domestics is to take the highest rated MCB and add this value to the test of the MCB values x 0.4
Looks like your client is setting up a small hair salon, which takes it into the commercial world. Watch out for the second and third hair drier being moved in at a later date !
The hair drier is likely to be used to set purms and the like so will be running for up to 3/4 hour at a time. plus all the other appliances so you will not see much change, if any, using a B32A breaker.
The lights will be on for the duration so that's another 3-4A FLC plus starting so that might well be a C6A
The shower has no diversity, although, at a guess, it will be only on for 5 minutes at a time. Still you wouldn't want to run the circuit hot - not good for impending assessments ! So that's a B32A.
If the whole lot was running at the same time it, as Biff55 says, will affect the volt drop.
I am not going to advise on the size of sub-main since there are other factors to be considered.
Reply to Maximum demand & Diversity lesson required please in the UK Electrical Forum area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...
Hi All Just looking for a 2nd opinion on cable sizing / breaker for a old cooker. The customer has had a 'Cooker Engineer' out to advise that...
5K
Hi all, I wonder if you might chuck in your 10 cents worth on this on? I have been asked to install electric heating in an office up on the 4th...
Toneyz
T