Scorpion90
hi to all .. to issue minor electrical work certificate.. should i do measurements from the consume unit to measure whole circuit or the or form the place where new work is done? lets say additional socket...
Zs from mid-point if RFC., end of radial if a radial. if measuring resistances, you measure the resistances of the whole circuit that you have altered.
the clue is on the ceret. it asks for "details of the modified circuit". not "details of the bit that you've added".
Firstly you have to make sure that the circuit you are altering/adding to, in your case an additional socket is:
a) capable of handling the addition i.e. is a a complete RFC as an example
b) is in a safe condition
What are your thoughts?
Is that all? have a think about what tests you need to do
Current GN3 p.102 gives the essential tests for the example of an extra socket outlet but admittedly doesn't tell you exactly how or where. Skin the cat how you like as long as it's safe and you cover all the bases I guess.
You have to confirm that the new addition is going to meet disconnection times, so that means measuring at each point on the addition to the start of the existing, this will be added to a Ze/Zdb at the source of the circuit being added to. With regards to IR however, just the new addition. Polarity will be taken at the point of addition and at any outlets/current using pieces of equipment on the addition.
When you say 'just the new addition' does that mean you would IR test just the circuit the new addition is on or literally just the addition?
GN3 does say "measure IR of the circuit that has been added to" (p.102) which I confess for a while I read as "the one that is about to be added".
An IR test would only need to be carried out on the addition to the circuit, not the whole circuit including the addition.
Well thats suprised me! How do you feel about adding to a circuit that may have poor IR (i.e less than 1Mohm)? Its a genuine question DS not meant in an inflammatory way. I have been testing the IR of the whole circuit that I have added to as that seems to make sense rather than adding to a circuit that is faulty.
I've always tested the full circuit too Steve not just the additions although Damian is right in what he says. Even though it sounds bizarre
the new wiring which you add isnt going to make the existing wiring any more crappy , nor are you obliged to take responsibility for it.
hence why a MWC doesnt ask you to test the entire circuit for an alteration / addition
Well, that does make sense Biff, but you've got the 2 comments above which suggest that an IR test of the circuit is required not on just the addition. 'Modified circuit' means the whole lot! However I haven't got GN3 so I'm just going on what the chap says.