That's fine mate, I don't take it that way
You are only responsible for
your work. As Biff says, a crap IR on the circuit you're adding to is technically no concern of yours as it doesn't affect the safety of your addition, however, as Trev says, you're more than likely to test the whole circuit A. as a matter of principle, and B. because it's often easier.
In most cases, if the IR turns out to be rubbish on the circuit then you're gonna go on to test just the addition, if that is fine then the work is signed off and you'd make a note that the existing circuit has issues that should be looked into. The customer has the choice at this point in time whether or not to have the existing IR issues looked in to as a seperate matter.
Remember however, if the existing circuit has problems that affect the Zs of the addition in a way that would make achieveing disconnection times impossible then these would need to be rectified in order to certify the work. Similarly, if you are planning on changing the protective device at the source of the circuit you are adding to in order to protect the addition, IR issues may have to be sorted in order to ensure the correct operation of the aforementioned device, therefore making an IR test of the
whole circuit a mandatory requirement instead of just an IR test of the addition.