Well thats suprised me! How do you feel about adding to a circuit that may have poor IR (i.e less than 1Mohm)? Its a genuine question DS not meant in an inflammatory way. I have been testing the IR of the whole circuit that I have added to as that seems to make sense rather than adding to a circuit that is faulty.
Hi Steve, that does seem a good practice, stick with it.:)
I've always tested the full circuit too Steve not just the additions although Damian is right in what he says. Even though it sounds bizarre
I expect he is Trev, but so far the evidence points to the circuit being tested. Is it stated clearly somewhere or is this just down to a skilled judgement?
Apparently GN3 has some info on the procedure on page 102 (I was told this in a PM) but I'm half cut and really tired so I just cannot be bothered to go and check it mate.
Sorry
You're not going to ever lose any marks for testing the whole circuit and as has been said it's good practice.
That's fine mate, I don't take it that way :)
You are only responsible for your work. As Biff says, a crap IR on the circuit you're adding to is technically no concern of yours as it doesn't affect the safety of your addition, however, as Trev says, you're more than likely to test the whole circuit A. as a matter of principle, and B. because it's often easier.
In most cases, if the IR turns out to be rubbish on the circuit then you're gonna go on to test just the addition, if that is fine then the work is signed off and you'd make a note that the existing circuit has issues that should be looked into. The customer has the choice at this point in time whether or not to have the existing IR issues looked in to as a seperate matter.
Remember however, if the existing circuit has problems that affect the Zs of the addition in a way that would make achieveing disconnection times impossible then these would need to be rectified in order to certify the work. Similarly, if you are planning on changing the protective device at the source of the circuit you are adding to in order to protect the addition, IR issues may have to be sorted in order to ensure the correct operation of the aforementioned device, therefore making an IR test of the whole circuit a mandatory requirement instead of just an IR test of the addition.
Well I'm off the bed but a quick flick through the OSG and the BGB seem to suggest an IR test on the modified circuit not just the addition.
BS7671 regulation 631.3 "A Minor works certificate may be provided for each circuit altered or extended"
OSG Page 166 Table G4.8 Part 3 (iii) "Measure the IR of the circuit that has been added to"
I really would value your thoughts Damian as you know what you're talking about and I'm just quoting words?
ooops.. just seen your response, will have a read :)
That all makes sense DS and you have justified it by using your professional knowledge, but do you interpret the above (BS7671 and OSG) in the same way as I do. If you do then would you say the regs are being over cautious by asking for an IR of the 'circuit'?
This is pointing to the need for seperate MEIWCs for seperate pieces of minor work on seperate circuits. For example, if you add a socket on one circuit and add a socket on another then you cannot use one MEIWC. In the required guidance attached to a MEIWC it states "This certificate has been issued to confirm that the electrical installation work to which it relates has been designed, constructed, inspected and tested in accordance with..."
The OSG is just guidance, it will cover it's behind where neccessary. It is not there to provide direct regulatory requirements, it is there to provide guidance, which if followed, will in 99% of cases conform with the direct regulatory requirements stipulated in the 'hard to understand' regs.
Think 25mm tails and 16mm earthing conductors :)
"To which it relates"... didn't see that bit.. thanks.
Very true.. You are correct and I am enlightened!
I'm still going to IR the whole circuit though :)
Thinking out loud here, what worries me a bit is that if you can't double-pole isolate the circuit under test and you don't open up the CU to disconnect the neutral for the circuit, then testing the circuit N-E or [L+N]-E (or L-E if the circuit has connected equipment on it) spreads N-E test voltage over the whole installation via the neutral bar(s). And then any connected equipment on other circuit(s) takes L-E test voltage to those circuit(s) (and elsewhere in the installation via the busbar(s) unless the relevant fuses are out or the MCBs closed).
Nothing gets the test voltage L-N but it does concern me if this is 500V, as it mostly needs to be. Particularly if something damageable has a functional earth, e.g. RCBO? Seems to me that effectively you have to accept you're more than likely testing much of the installation [L+N]-E whether you mean to or not.
That's unless you disconnect the circuit neutral which means open up the CU when maybe you didn't otherwise need to, and that brings its own aggro and risks (cover may break/not want to go back on, messing around pulling circuit neutral out near live tails [E@WR], may be a pain if the CU is absolutely chocker, etc.).
Probably overthinking as usual :)
Disregarding the current discussion for a moment, if you are going to IR a circuit on an operational board then of course you are going to disconnect the neutral aren't ya.
I can't think of an instance off the top of my head, where it wouldn't be just as easy to test the circuit as a whole, as it would to fluff around to just test an addition to the circuit!! No brainer as far as i'm concerned, test the circuit as a whole... End of!!
An addition to a circuit that is fed by a board that cannot be isolated for whatever reason. IR and R1+R2 the addition, R2 the existing.
90% of the time you're right, it's common sense, but life ain't black and white, it's 50 shades of grey too, ooh err ;-)
I always test the Zs where the modification is about to be made, so that I know I have continuity of R1 + R2 - then do the work and test from the CU.