Do you think that maybe the method shown in the article is recommended if a time delay trip is not installed on the submain, to avoid nuscience tripping?
Don't worry about linking the outbuildings EMT to the MET it's all part of single sourced TT installation, and should be linked
Generally speaking, a time delayed 100/300mA RCD located at the supply end of the installation will effectively avoid nuisance tripping of any 30mA RCD's located at the load end of the sub-main. This will be in addition to providing added earth fault protection to your TT system...