Quick Question. Despite being 50 I am a newbie electrical installer. Preparing for my retirement from public service. Anyways - my Question. How the hell do MCBs work on a TT system. Say Ze is 33 Ohms with a 240 supply the PFC will be just over 7 Amps. How does that trip MCBs or is there were the importance of RCDs come in. Can someone explain??
 
In many instances ADS wont be achieved and must be satisfied by other means.

I don't mean to seem disrespectful (especially as I'm an apprentice only a few years younger than you), but this should have been covered at length when you were training.
 
You need to study the curve and in most cases a very low fault current won't trip an mcb , maybe a 6amp but not much else certainly not fast enough to achieve ADS

This is why TT installs had upfront RCDs Or Voltage operated earth leakage devices or what ever they were called back in the olden times
 
In many instances ADS wont be achieved and must be satisfied by other means.

I don't mean to seem disrespectful (especially as I'm an apprentice only a few years younger than you), but this should have been covered at length when you were training.
Thanks. 28 years ago I sparked but on aircraft. Avionics to be specific. Have HNC in EE. My DEI course was basic and in no way do I see myself as a Electrician. Yea we covered the OSG in alot of detail and there was nothing about TT values apart from needs to be under 200 ohms Ze. I suppose I get credit for coming up with the question. Like you and (prob more than you)I have alot to learn 😆
 
Thanks. 28 years ago I sparked but on aircraft. Avionics to be specific. Have HNC in EE. My DEI course was basic and in no way do I see myself as a Electrician. Yea we covered the OSG in alot of detail and there was nothing about TT values apart from needs to be under 200 ohms Ze. I suppose I get credit for coming up with the question. Like you and (prob more than you)I have alot to learn 😆
The best of us admit that we ARE ALWAYS LEARNING.

I have only ever met a couple of sparks who were sure they knew it all.
strangely enough I didn’t get on with either of them very well.😆😆😆
On that basis James we’ll get on like a house on fire 😂
 

Reply to MCBs ADS in TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
916
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
1K
Good Evening All, I'm not an electrician but I'd like to pick the brains of those that are please. Note I intend getting a qualified electrician...
Replies
0
Views
977
Hi everyone I asked my assessor about touch voltage and he was not keen on explaining properly and gave me a rough answer which made me think...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock