Hi all,

In general do you size the cable to the MCCB full trip setting rather than the adjustable setting for the load being supplied. In some cases upsizing the cable can be costly even from 320/400. One of the site engineers is adamant that it should be sized for full trip setting.

I'm not sure I agree and have rated the cable for the adjustable setting many times previously. What are the views on this.

Thanks

R
 
The reason for using an adjustable MCCB is often that you need a non-standard protection requirement. Turning down the thermal trip point is the most common option, but you also have short-time trip settings on some and possibly EL trip settings as well. All of those impact on what cable(s) are acceptable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
MCCB Adjustable trip setting - cable rating
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
RobHol,
Last reply from
pc1966,
Replies
3
Views
1,974

Advert

Back
Top