Hi all,
using my megger to measure Zs at furthest socket on garage radial, unit shows flashing/ bleeping voltage of 240v with all 3 neons lit at top for polarity, has anyone come across this? I have checked the circuit and and all conductors run from the garage cu correctly to each socket.
Also doing ins resis test between line and neutral at the cu on one ring the megger just flash's o.oo?
would appreciate explanation
regards
Naz