Naz

Hi all,

using my megger to measure Zs at furthest socket on garage radial, unit shows flashing/ bleeping voltage of 240v with all 3 neons lit at top for polarity, has anyone come across this? I have checked the circuit and and all conductors run from the garage cu correctly to each socket.

Also doing ins resis test between line and neutral at the cu on one ring the megger just flash's o.oo?

would appreciate explanation

regards

Naz
 
Hi all,

using my megger to measure Zs at furthest socket on garage radial, unit shows flashing/ bleeping voltage of 240v with all 3 neons lit at top for polarity, has anyone come across this? I have checked the circuit and and all conductors run from the garage cu correctly to each socket.

Test automatically inhibited by MFT because it has detected a voltage between N-E.

Also doing ins resis test between line and neutral at the cu on one ring the megger just flash's o.oo?

Test automatically inhibited by MFT because it has detected an external voltage >55V present at the terminals.

would appreciate explanation

regards

Naz

Hope this helps mate. Note in the first case if the E or N connections are poor the MFT may be fooled into believing there is a voltage between N-E where there is none. This could just be caused by tarnished contacts on the garage socket(s), try plugging and unplugging several times and retest, or probe the terminals on the back of the socket.
 
Last edited by a moderator:
check voltages at the garage socket/s with the MCB off. could be a cross connection from another circuit.
 
hi all

thanks for the pointers, checked the various things, tracked it back to the earth at the home consumer unit, this has been crimped/ extended to the CU and had come adrift, reconnected, megger now showing correct connections and getting decent loop imp and measured Zs values.

One issue i could use help with, one of the ring mains is showing very low IR results between L-N conductors, have looked at ever socket, all wiring looks ok, connections not loose or screwed onto pvc sheath, nothing plugged in or neons etc, the only thing ive noticed is the hall socket has had water ingress over the years from the shower room the other side of the wall, i cut the wires back a bit and cleaned up the ends, refit and tested again but same low results. Could water ingress be the issue along with the cables oxidising? Mentioned it to customer, wasnt keen on rewiring that section. Would I note the results on the cert and include an advisory note to cover myself?

as always your attention much appreciated

Naz
 
what do you call a low reading? some guys are not happy if they get < 1 zillion ohms.
 
well to be honest around 1Meg. I know the book states 2meg but to investigate anything less.

regards
 
that could well be a bit of damp. try doing a few tests, 1 after another. the applied voltage coud dry it out, if it is damp and your readings will increase.
 
thanks,will try when next over there, customer tells me he has had water soaking through the wall on a number of occasions. What do you think to my point about putting the advisory note on the cert if he doesnt want to suffer the cost of any poss remedial action to cover myself
 
well to be honest around 1Meg. I know the book states 2meg but to investigate anything less.

regards

Have you isolated each run of cable and tested individually ? that would narrow it down a bit !!
 