Discuss Meggering of 3-phase Synchonous Generator in the Industrial Electricians' Talk area at ElectriciansForums.net

S

speedtronic

For phase to phase Meggering of 3-phase Synchonous Generator, we have to open its flexible links (between phases) & its star point. We then connect Megger's positive lead to phase (which we want to Megger) & we short remaining two phases with ground?(& connect megger's negative lead to it) Why?? What if we donot short other two phases with ground?
 
For phase to phase Meggering of 3-phase Synchonous Generator, we have to open its flexible links (between phases) & its star point. We then connect Megger's positive lead to phase (which we want to Megger) & we short remaining two phases with ground?(& connect megger's negative lead to it) Why?? What if we donot short other two phases with ground?

erm...nothing. All you are doing is IR checking between output windings. This is the same as, say, connecting together live conductors on an installation and IR checking between them to earth. If there is a fault there it will show up if you do them connected or IR test individually:)
 
please tell me that for phase to ground meggering of a 3-phase power T/F. Do we need to perform same practice? I mean like shorting of other two phases to ground?
Moreover, kindly tell me something about high pot. test. I know that it is used to measure maximum voltage withstanding capability of an equipment. BY injecting high voltage, what do we measure at output? & what should be its range?
Also kindly tell me about stator winding inter-turn faults? what they actually are? As I know, In case of inter-turn winding fault the current on both side of the winding is same so differential protection can not be used? then what kind of protection is used for it?
 

Reply to Meggering of 3-phase Synchonous Generator in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
489
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
484
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
539
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
621

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock