When you say a customer has rewired their house...do you mean you have rewired it or they have
The customer rewired it, I came in and gave him the routes and did all the bonding. But suddenly he decided he wants his incomer moved because the store cupboard its in now, is where he wants to put the stairs for his loft conversion.
He's a civil engineer so was quite good at construction work.
 
DNO fits Cut out and seals, MOP fits meter and DPI but leaves CU tails disconnected, seals everything except DPI load terminal cover is plastic seal. Cut out to meter tails normally 3 metres maximum. Electrician then tests and connects to DPI.
 
Death tests are a common think, I do one once a month for places where either tennant went arround the meter (and got caught) or ex weed plantations. You will state death test in limitations and use lim where not applicable. If you use software for certs you can even skip wrong questions. Add into notes that instalation is safe to energize for further testing, but futher test are necessary "After supply is provided" to acess condition and assure safety of the continued ussage of installation.
Then as stevels4 said they will move the supply and you can inspect the rest.
I find limiting or disconnecting most of the circuits "for the duration of the work" is useful, SO you wont have to do schedule of test results for too many circuits twice... (you do actually need to prevent its energisation for this)
 