Thats true about not being policed, with a lot of self connect meters/ isolators.I have seen a run well over 15meters tails+earth in copex.It’s the DNO’s fuse for protecting their equipment, not for protection of the consumers side, other than what they allow which is typically 3 meters.
Not that they police it mind.
I also wouldn’t code it on an EICR tho for tails longer than this, provided that the fuse offered fault protection.