S
sparksburnout
I had a discussion only the other day with a guy from WPD's technical team who made it very clear that their cut-out is there to protect their equipment and not the meter tails. They allow tails of up to 3M (From the cut-out not the meter) to the CU to be "additionally protected" by that fuse, but anything beyond this must have additional protection and conform to BS7671. His words not mine, although it seems pretty simple to me.

