I had a discussion only the other day with a guy from WPD's technical team who made it very clear that their cut-out is there to protect their equipment and not the meter tails. They allow tails of up to 3M (From the cut-out not the meter) to the CU to be "additionally protected" by that fuse, but anything beyond this must have additional protection and conform to BS7671. His words not mine, although it seems pretty simple to me.
 
Of course, we are then in the scenario, of having two fuse in series, probably of the same rating (or of a size not to allow suitable discrimination, without reducing supply for customer), and it will be the ---- of a coin which will go first.

Never really understood this scenario, even though eminent members have explained it several time before for me :)
 
Of course, we are then in the scenario, of having two fuse in series, probably of the same rating (or of a size not to allow suitable discrimination, without reducing supply for customer), and it will be the **** of a coin which will go first.
Never really understood this scenario, even though eminent members have explained it several time before for me :)

There is and never has been any requirement to provide discrimination with the supply fuse
I can't see it would matter in the very rare circumstance which one popped, they are going to be off supply anyway

The above assumes a single user supply rather than a multiple sub main installation
 
So apart from the DNO requiring such, does it actually make any difference, i.e. prevent the Main Fuse going before the switch fuse, or are we just on about complying (BS7671 et al)?
 
If there were a 100 amp fuse in the cut out and we had to account for discrimination,we would end up putting a 2 sizes lower fuse (63A )to have any chance

The client could become unhappy losing a fair portion of their capacity for no apparent benefit if that was the case
 
I think the 3m is an historic answer to our question. There needs to be a limit so DNO fuse will melt when required, and with TNCS and 25mm tails I think technically it could be a lot longer than 3m. For example 88-2 80A fuse needs 400A to melt in 5 sec, and this is a fault loop of no more than 0.575 Ohms at 70C. DNO quote 0.35 Ohms as max for TNCS so 0.575-0.35 = 0.225 Ohms left for tails. So assuming 25+16 is 0.875+1.4x0.8 = 2 mOhms per metre. And so tails 100m long would still provide ADS, unless I've messed it up (always possible). This was just out of interest and it's DNO call anyway. o_O
 
If there were a 100 amp fuse in the cut out and we had to account for discrimination,we would end up putting a 2 sizes lower fuse (63A )to have any chance

The client could become unhappy losing a fair portion of their capacity for no apparent benefit if that was the case

So the point of putting a 100a switch fuse after a 100amp cut out fuse is?
 
So the point of putting a 100a switch fuse after a 100amp cut out fuse is?
I think the point, is that the DNO have no control over what may be installed beyond the meter. Some numpty might come along and run a bit of bell wire to a DB for all they know. In the case of a switch fuse 4M from the cutout then under a low impedance fault then obviously both devices are going to go, even if it is as low as 63A. They are trying to put the responsibility on the installer to make sure the cables beyond their equipment are adequately protected, which their fuse may not?
 