gus4098
i have just purchased a new metrel 3002 multifunction meter, thought i would try it first on some test cables 10m of 4mm T&E insulation test, the readings i got were 8.8 M ohms approx across all cores, then tested with my kewtech kt64 and readings were what i expected >200Mohms on 250 volt setting.
can anyone tell me if i am being dumb and have the setting all wrong , if not the meter must be faulty
can anyone tell me if i am being dumb and have the setting all wrong , if not the meter must be faulty