gus4098

i have just purchased a new metrel 3002 multifunction meter, thought i would try it first on some test cables 10m of 4mm T&E insulation test, the readings i got were 8.8 M ohms approx across all cores, then tested with my kewtech kt64 and readings were what i expected >200Mohms on 250 volt setting.
can anyone tell me if i am being dumb and have the setting all wrong , if not the meter must be faulty
 
I have a Metrel and I wish I'd not bought it.Instructions are awful Readings can be all over the place. Is it me or is it the machine?
 
I've got a Metrel and not experienced this.

Out of interest did you test the cables "as one" i.e. connecting all 3 cables and letting the machine "step" around the combinations or did you do them individually?
 