Homeowner wants to upgrade their CU. Ex-council house in a block still owned by Islington Council. Main incomer is a modern 3-phase TNCS going into a Ryryefield board. Each 60A fuse then feeds a different apartment with a single core orange sheathed MICC cable. The earth pot is terminated into galv trunking within the property, and then a clamp on the sheath is providing the neutral for the meter. As such the supply is TNCS, however as it is before the meter it is likely owned by the BNO (Islington Council).
I spoke to the NICEIC technical helpline and they think that this is non-compliant and should be a C1, as a PEN fault would energise everything metal in the entire apartment block.
The only ay to resolve this would be to run new 3-core SWA to the apartment. However, given the block is owned by Islington Council, they must be EICRing all of the other apartments/communal areas and passing them despite this TNCS setup.
What would you do in this situation? I'm thinking contact the council and ask for written confirmation that they are aware and that they deem it safe/accept liability?
Would you proceed with a new CU install in this instance, obviously noting everything on the EIC?
I spoke to the NICEIC technical helpline and they think that this is non-compliant and should be a C1, as a PEN fault would energise everything metal in the entire apartment block.
The only ay to resolve this would be to run new 3-core SWA to the apartment. However, given the block is owned by Islington Council, they must be EICRing all of the other apartments/communal areas and passing them despite this TNCS setup.
What would you do in this situation? I'm thinking contact the council and ask for written confirmation that they are aware and that they deem it safe/accept liability?
Would you proceed with a new CU install in this instance, obviously noting everything on the EIC?