I would personally do a Minor Works with the full scope of required tests with the Zs at the extremity to ensure fault protection and earth continuity is maintained throughout. You do not want to be in a situation later down the line if something were amiss and you, being the last person to work on it were to have accusations aimed at them. One or fifty Minor Works should not be a deciding factor.
 
I would personally do a Minor Works with the full scope of required tests with the Zs at the extremity to ensure fault protection and earth continuity is maintained throughout. You do not want to be in a situation later down the line if something were amiss and you, being the last person to work on it were to have accusations aimed at them. One or fifty Minor Works should not be a deciding factor.
True but I would always document my scope of works that I have covered in the description and comments section and record N/A in the schedule of inspections which is as it states is not applicable

Too be clear I would only provide the EIC if I thought it was necessary, not because I've installed say 2 sockets it would depend on the amount and the scope of works involved to justify it.
It still complies in my eyes
 
Circuits to bathrooms rcd protected as an example if I have not worked in the location or the circuit
 
It is a regular thing that a works will include both new circuits and alterations to existing. I would always include the altered existing circuits on the same schedule as the new circuits on an EIC.
All that is required is to state on the circuit ID....(example).
Cooker (new circuit)
Upstairs lights (existing circuit)

As long as the description of work is comprehensive I think this is perfectly clear, our NICEIC inspector has seen dozens of EIC's covering both new and existing and never commented.
Why complicate things and add to the worlds paper mountain by completing a wad of minor works when a full EIC has to be issued anyway?
 
I think the main fact is that the work has the correct testing carried out what ever certificate the electrician deems applicable to the work undertaken.
 
I think the main fact is that the work has the correct testing carried out what ever certificate the electrician deems applicable to the work undertaken.
Minor New Works. "Addition and Alterations to an installation that does not extend to the provision of a new circuit" In today's view of quoting the BYB this come from "Definitions" couldn't be clearer really could it? To stop any further arguments, can I suggest that every one reads page 418 BYB Appendix 6 page 413 BYB in today's black an white world, there it is in Black and White, not going to argue anymore, I'm out.
 
Point (v)
Electrical installation certificates will indicate the responsibility for design,construction,inspection and testing whether in relation to new work or further work on an existing installation.

The Minor electrical works note in bold on page 417 is simply indicating that it cannot be used for a provision of a new circuit.
 
Earlier this week I installed a shed supply, took a 4mm SWA from the existing ground floor RFC via an isolator and fitted 2 x double sockets and a 5' striplight via a SFCU in the shed. So this is an addition to an existing circuit technically, MWC or EIC ? :)
 
Earlier this week I installed a shed supply, took a 4mm SWA from the existing ground floor RFC via an isolator and fitted 2 x double sockets and a 5' striplight via a SFCU in the shed. So this is an addition to an existing circuit technically, MWC or EIC ? :)
Whatever you feel is appropriate dave as long as it's certified :)
 