Been asked to move a consumer unit by a local estate agent as ( believe it or not ) its tucked behind a kitchen unit , only accessible by taking part of the kitchen out! , it's an old rewire able fuse board , if I am to move it, would I be required to change it to an updated rcd protected version? Or if the fuse boards still in good shape could I re-use?
However chances of that are slim to zilch.if the new cables used to extend the existing circuits are buried less than 50mm in the wall then rcd protection will be required.
if in surface trunking or similar , then no rcd is required and you can re-use the rewirable CU.
there is no requirement to install a new rcd CU just because youre moving the old one.
As such, it will not comply with the regs.
Disagree. Moving it is reinstalling it, once you disconnect/reconnect circuits. As such, it will not comply with the regs. Additionally, an upfront RCD cannot be fitted either if compliance is required.
what does it say in BS7671....Guys I seem to remember that if you are moving and extending circuits then the whole installation needs to be brought up to date. Now from my dealings with the old 3036 fuses there was a fair few of lighting circuits that had no earth so these would need rewiring. Also putting a rcd at source doesn't comply with the 17th .
I have to say I have never moved an old 3036 board and not replaced it, seems alot of work to do not to upgrade but regulation ?
yes and if theres any doubt as to its suitability for continued service...then a visual inspection + PFC would confirm....either way...thats because bs7671 recognises that a rewirable CU is a perfectly acceptable piece of equipment to use rather than use it as an excuse to fleece unsuspecting customers.
agreed I will give option from now on, I unfortunately do a lot of domestic these days :93: