Hi,


I am currently training to become an electrician. I have passed all relevant C&G level 2 exams along with C&G level 3 inspection and testing and principles of electrical science.


I have been asked to help design some garden circuits but been given specific instruction on how the circuits will be protected.


Could you please give me feedback on the attached plan.

Specific questions are ;


1) If the 4mm2 cores of the SWA have a current carrying capacity of 37A, can I use only 2 cores for my neutrals and 4 cores on separate circuits.


2) Are my earthing arrangements correct? i.e. 4mm2 through the house then using the SWA armour as the earth to the front gates.

Multi-core neutrals and earth Planning stage - EletriciansForums.net
 
S

Silly Sausage

I would be installing DBs in the shed and green house, supplied with 2 or 3 core SWA, and local RCD.

For the gates, again, probably be a local (to the gates) DB because you're going to require an enclosure to split your 7 core into the individual circuits anyway.
Whether I'd have the RCD there or back in the house, hmmm, depends on inconvenience level if it trips.
 
OP
G

Gigsy

-
Reaction score
46
Each circuit must have its own seperate neutral, sharing a neutral between circuits is very dangerous for anyone working on these circuits in the future.

It is more of a parallel conductor design than being a shared neutral in my opinion. The person I am working for is electrically qualified and this is how he said we wire it. I am unsure that is the reason I am asking here.

In this configuration it is impossible to get a dangerous voltage on the neutral so long as the neutral is terminated in the consumer unit, same as any circuit. It is not like a situation when you borrow a neutral from a different lighting circuit. It is not a dangerous configuration.
 
OP
G

Gigsy

-
Reaction score
46
Apart from the shared neutral being dangerous, which I do not think it is in this configuration, is there any reason why we could not wire it as shown?
 
OP
G

Gigsy

-
Reaction score
46
I know of configurations in which sharing a neutral can result in a dangerous voltage on the neutral. I knew this thread would go down this path. I could draw the situation, can you? If so draw it then explain how the fault relates to this design.
 

Reply to Multi-core neutrals and earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

JIB Electrotechnical Certification Scheme (ECS) is a nvq3 and am2 all i need?
Evening all! im looking at progressing and trying to obtain a JIB gold card but unsure what i need altogher. i currently have C&g 2330 level 2...
Replies
1
Views
355
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
1K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
6K
Hi I'm Charlie, I have recently done my 18th edition and got enrolled on night classes for Level 2 C&G Electrical intallations. I currently work...
Replies
0
Views
392
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
532
Advertise Here

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top